I put an Anode in a steam boiler
jhewings
Member Posts: 139
Two years ago.
0
Comments
-
Looks like I could have changed it last year0
-
I'm not a pro, please explain to me like I'm 5 (ELI5), why would you do that? Does it really help slow corrosion?0
-
I did it because I saw an "installation tips" from a boiler manufacturer (US Boiler I think) which said "consider an anode". I am not sure what is the significance of the condition of the anode after 2 years. i guess I was worried because I had previously rerouted 2 out of 26 radiators with copper connected directly to black iron and the connections are now hard to reach.0
-
Hello @jhewings,
Wow I don't think they get used up that fast in a hot water tank. I wonder if you maintain a good anode rod if it will extend the life of the boiler.
I would think with a lack of fresh water it would last forever.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
MikeAmann said:
Try a powered titanium anode. It does not get consumed and has a forever warranty.
I will give you a link if you ask.
I would love to use one on my water heater, but I wasn't able to find one compatible with Bradford White heaters where it's combined into the outlet.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Hello @ChrisJ,
https://www.waterheaterrescue.com/products/powered-anodes-for-sale.htmlChrisJ said:
I would love to use one on my water heater, but I wasn't able to find one compatible with Bradford White heaters where it's combined into the outlet.MikeAmann said:Try a powered titanium anode. It does not get consumed and has a forever warranty.
I will give you a link if you ask.
There may be others out there. I have not tried one.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
I wonder if it provides any protection to prevent the boiler rotting out above the water line.
Also I wonder since hot water tanks are typically glass lined minimizing the Cathode material area anode rods last for years. Boilers are not glass lined so there is an overwhelming amount of Cathode material exposed to the boiler water.National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Hi @109A_5 , Anodes can only protect what they can electrically "see". Anything above the water line is invisible to an anode. Also, think of the anode as a long skinny light bulb. It protects best what it can light up directly. Nooks and crannies don't often get good protection. Also, you nailed it with the mention of relative area. Anodes work nicely when consumed slowly, as in a glass-lined tank, with little exposed steel. With all that cast iron, the anode has to be consumed quickly, producing hydrogen gas and some corrosion byproduct, which likely don't help things.
Yours, Larry1 -
Hello @Larry Weingarten,
The reason I wonder about above the water line is two things. First, that is a steam boiler high failure type situation. And second, although I do not know how that anode rod was mounted in that steam boiler it looks all depleted all the way up to the mounting. I assume it was inserted vertically like a hot water tank in which case part of the anode rod it would only be exposed to steam, yet it is all depleted. Maybe the steam washes the material down into the water over time. Maybe it was mounted horizontally. I wish @jhewings would post more about the situation (good or bad).
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
The anode was mounted horizontally in the tapping opposite the return.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements