Radiator Sizing
Nate0846
Member Posts: 7
I have a radiator I’m trying to calculate the EDR for and I’m coming up with nothing. Can some one point me in the right direction?
0
Comments
-
I think found a match. If I use the old column style and call it 5 columns and use the 14” height and 12 1/2” width it comes up with a 4. So I will multiply that by the sections and hope it comes out correct. This is a water boiler that I think was converted from steam.0
-
I wouldn't do that. Inaccurate. Instead do you see any embossed writing on it anywhere? If you can provide a manufacturer name, I might be able to help. Sometimes you'll find that around the tapping where the valve is attached in that picture or on the other side. It might also be on the columns of the first or last sections. This looks similar to a Zenith made by American Radiator, but it's not quite the same. When was your house built? Do you believe that rad is original to the house?1
-
No embossed writing on it that I could see. The house was built 1900 and yes it appears to be original to the home.0
-
I would take a second look with a flashlight. Look all around. Maybe you'll luck out. I couldn't find anything. Maybe it's in Dan Holohan's EDR book? If I had to guess, I would say it's between 3-4 sq ft/section, but those are steam ratings. You then need to convert to forced hot water ratings, in which case, the right way to size the boiler, if that's what you're trying to do is to perform a Manual J calculation for your house. Or is this for some other reason?0
-
It’s for a client I’m working on to quote a new boiler. I’ve looked throughly for any markings and couldn’t see anything. 😔0
-
I'm not a pro by the way. Just like digging up info online. Aetna Flue Window Radiator, made by American Radiator Company. You were spot on. 4 sq ft/section.
https://babel.hathitrust.org/cgi/pt?id=uc2.ark:/13960/t83j3bp53&view=1up&seq=85&q1=aetna
56 total.
At the risk of telling you something you already know...Since it's painted bronze, the effective EDR will likely be 10-20% less. Not sure if you're installing a steam or hot water boiler...
https://heatinghelp.com/heating-museum/does-the-color-of-a-radiator-matter/
2 -
Are you sizing the water boiler from the system EDR?Nate0846 said:It’s for a client I’m working on to quote a new boiler. I’ve looked throughly for any markings and couldn’t see anything. 😔
0 -
@Nate0846, that looks like the American Radiator Company's Aetna Flue Window Radiator seen here in The Ideal Fitter (1911):
President
HeatingHelp.com1 -
Sorry @random12345. I missed your comment about about the Aetna above. I guess I was too excited to visit our library.
President
HeatingHelp.com1 -
-
@ramdom12345 Thank you! Pro or not I greatly appreciate you digging that up for me! I’m glad I was accidentally on track when calculating it. 👍🏻
To be honest I did not know that the paint affected the the EDR. 😳
I’ve been getting more boiler quotes due to one of our designers retiring so I’m seeing more than I used to. Thank you for the link!
@KC_Jones this is for a water boiler and I’m taking the radiators in to account and the load for the house for a comparison.
@Erin Holohan Haskell thank you so much for digging that up for me! I will be buying that book and keeping with me!
I greatly appreciate all of your help everyone! 🙌🏻1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 919 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements