Kewanee Water Boiler.....How does the floor look??
JUGHNE
Member Posts: 11,276
This is a 1961 3 pass fire tube NG fired boiler.
Was oil burner for it's first +20 years.
It is 23.6 HP, max 990 MBH. Series 5X....size 3R6F O
Has an Adams "Speedflame" power burner from 1997.
HP 800 is rated from 300,000 to 800,000 BTUH.
Presently down fired to 327,272 BTUH.
Install book says to have burner tube at least 7" above floor it is only 6".
The floor is disintegrating the worst just under the burner at the front of the fire box,
where the screwdriver is stuck.
Any ideas or...... don't worry.
Thanks for looking.
Was oil burner for it's first +20 years.
It is 23.6 HP, max 990 MBH. Series 5X....size 3R6F O
Has an Adams "Speedflame" power burner from 1997.
HP 800 is rated from 300,000 to 800,000 BTUH.
Presently down fired to 327,272 BTUH.
Install book says to have burner tube at least 7" above floor it is only 6".
The floor is disintegrating the worst just under the burner at the front of the fire box,
where the screwdriver is stuck.
Any ideas or...... don't worry.
Thanks for looking.
0
Comments
-
Is that a brick floor? If yes, don't worry about it. The down firing will help.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
No bricks that I could find.
It has been downfired for quite a few years...maybe 10 or more.
Just some layer of something what seems to be poured like concrete many years ago.
Most likely has asbestos (1961) in the mix.
I have thought of maybe firebrick on the floor, at least in the front.
Or even a layer of sand....what would that be like?
It is a wet leg boiler....I don't think it is a wet base.0 -
It's probably "castable cement" You buy a bag, mix it with water. It hardens when you fire the burner or until it dry's. Any refractory supplier would have it. They sell many different temp ratings.
Your floor doesn't look to be deteriorated enough to do anything about it but maybe the picture is deceiving, and it probably does have asbestos.
The book says 7" tube height, but they only give you 1 height......that is for the maximum firing rate. If you were too close to the floor you would get black carbon from impingement.
1 -
By Brick, I meant a custom castable Fire brick type material (hard), as opposed a ceramic fiber blanket type (soft) floor. Not actual 2.25" x 4.5" x 9" fire bricks. sorry for the confusion. I believe it is hard castable material. Am I correct?
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The floor used to be quite solid.
It looks to have been poured.
About 12 years ago I even vacuumed debris off of it.
You would not try it today as it is crumbly.
This gets opened every 4 years.
The future of the building and this boiler is uncertain.
Won't be torn down but someone may get the FAF bug for something else.
One "professional" construction manager told the owners they could not use it for day care as "steam" was too dangerous.......it is a hot water system with commercial grade child proof convectors etc.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements