Radiant Heat Loop
rmorrisjr24
Member Posts: 3
Hello, I have a boiler with multiple zone valves that feed radiators with one main circulation pump on the supply side of my boiler. I added a radiant loop with a mixing valve with an additional zone valve. My question is, do I need a separate circulating pump on the mixed side of the mixing valve that feeds my radiant loop?
0
Comments
-
Possible to make a sketch or post some photos ?30+ yrs in telecom outside plant.
Currently in building maintenance.0 -
YES. You need to get the mixed water to flow out of the mixing valve. The system pump can't do that.
I have also found that you probably didn't need the zone valve. I did the same thing 20 years ago. Had a zone valve for future use when I installed my Buderus Boiler. 2 years later I installed some radiant floor heat with a mixing valve and pump. About 10 years ago I had a Zone valve failure and used the radiant zone to fix the problem temporarily. Turns out the thermostat operates the pump and heats the radiant room. When the circulator is off the room heat stops. So I never put the replacement head back on that zone. Still on the shelf for future use.Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Here is drawing, it’s a little crude, but should give the info needed.0
-
yes, you need that pump there,known to beat dead horses0
-
You need a pump, one with an integrated check valve, then you would not need the zone valveBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Thanks guys!0
-
Question about this application guys. When piped in this fashion with pump w/IFC after the mixing valve. Will both pumps need to operate simultaneously in order to heat the radiant zone or can the radiant pump heat this zone independently.0
-
This article show 3 options for adding a small radiant zone to a high temperature boiler system.
https://www.pmmag.com/articles/84495-a-little-floor-warming-please-john-siegenthalerBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements