staple up radiant with carpeting????????
EternalNoob
Member Posts: 42
Brainstorming how to reduce noise between two floors of split-level duplex, both floors with radiant. Upstairs has radiant staple-up to hardwood floors and footsteps propagate a lot to downstairs. Have already done insulation btwn bays and sound-proofed ceiling assembly. Considering doing wall to wall carpet over hardwood with carpet padding to reduce noise. Kind of assuming that this would render the radiant ineffective, but i'm wondering if anyone on here has seen it done successfully? Is there a such thing as a carpet pad with good sound reduction but but low R-value?
0
Comments
-
What supply temperature are you running now. Does the floor heat the space adequately on the coldest days?
Here is what carpet and pad will do to the output. So the question becomes ho much hotter will the supply need to be and is that acceptable? 140F is about as hot as you want to run staple up against wood.
So you would want to know the heat load of the room, then crunch the numbers to see it it can work out, safely and comfortably.
There are some radiant specific pad, but probably not much sound barrier.
Buy the tenants thick soled slippers
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
My outdoor heating curve max's. out at 130° water temperature and when I've hit that in the past, my hardwood has split in places. Try to stay below 120°.
However, the max. water temperature can depend on the plates used. Loose fitting plates can run hotter.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Thanks guys. Mostly i just wanted to know if this was a ridiculous idea or not. I have been running 110F and the ability to heat the space on the coldest days has been plentifully sufficient here in Northern California. If I'm abandoning the hardwood then i suppose the wood splitting from higher temperature fluctuations will not be a concern, so running 120 makes sense if i need to.0
-
So 3/4 sub floor and 3/4 hardwood now? = R 1.8
1/2 bonded foam pad is R 2.0. 1/2" rubber is .6.
Carpet can run 1-2 R
No doubt the thicker pad would offer more sound deadening. That rubber "radiant" pad is fairly hard.
You carpet pad temperature rating may limit how hot you can run the floor, and thus the BTU you could expect.
Hopefully it is a low load areaBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements