How to test Conbraco size 1 relief valve?
ilikebeans
Member Posts: 18
Any ideas how to test this relief valve?
I pushed and pulled up and down on the stem part and it doesn't move much either way.
Thanks.
I pushed and pulled up and down on the stem part and it doesn't move much either way.
Thanks.
0
Comments
-
-
mattmia2 said:replace it. It looks like there was some sort of a lever that pushed on something inside that stem but in addition to being 70 years old and having a high likelihood of failure based on age alone, it also likely doesn't meet modern relief valve standards.
Is this as simple as replacing a vent on a radiator? Just screw the old one out and new one in?
What could it be replaced with?
Thanks.0 -
There is a handle missing. The handle is not just a small flat metal blank with a hole in it like the lever on an auto feed valve (Pressure reducing valve). This is handle has a detailed lever shape that fits in the slot of the vertical valve stem. The other end of the handle will rest on the side of the relief valve. When you pull up on the missing handle the lever action will have a mechanical advantage that will lift the stem. Since this has obviously not been operated or tested in many years, if you are able to open the valve to test the operation, The valve most likely will not seat properly and you will need to replace it anyway.
Good luckEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
I thought you were supposed to replace these every few years as a matter of course. I can’t remember where I read that, but I replaced mine last year because, as far as I know, it was as old as the boiler.Conbraco is now owned by Apollo Valve. I looked up the application in the Apollo catalog and ordered an Apollo Valve 13-510. It’s supposed to open at 15 PSI, though I don’t know how you’d test that. The only test I know of is to pull the lever and see if steam comes out.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
It just unscrews and you screw a new one on. Pay attention to pipe size and gender. Use teflon tape or dope or both. Relief valves are available with male and female threads. You might need a nipple or a coupler. The discharge should be piped to the floor with pipe rated for the temp of the fluid in system with the open end unthreaded. The pressure has to be at or below the rating of the boiler and the discharge capacity has to be greater than the input of the boiler.1
-
-
size the replacement by the btu Rating, not necessarily pipe size
Also the valve needs to be mounted verticallyBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream2
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements