Carlin gas control model 60200fr

hwesley
hwesley Member Posts: 1
edited September 2022 in Gas Heating
Encountered problems ever since we bought our house.  Previous owner converted an oil burner to gas to hot water that we use for our heating and domestic hot water. We continually get lockouts.  Again, novice with no hvac experience here.  Had several companies come and essentially put band aids on the system.  
Let me generalize, there’s a call for heat, sounds like the system wants to flame to fire up then shuts down and I’m left with a continually sound of gas or air being forced into the boiler.  Solution has been to push reset button and that has worked 99% of time.  Tonight I got this message for first time “ua low ck frod”  then kept getting “recycle” and “recycle limit”.  I could not get system to shut off so I literally turned off power to unit waited a minute and turned back on and now it displays “stand by”  which I understand is a good thing.  Sorry for length of post and thanks in advance for any help.

Comments

  • pedmec
    pedmec Member Posts: 1,027
    microamps too low. check flame rod. that is your error code. remove flame rod and clean, also inspect for cracks. reinstall and check microamps during start up. it is sometimes easier to just replace while you have it out but cleaning is all it needs most of the time. also make sure you ground wires are all secured
  • 109A_5
    109A_5 Member Posts: 1,501
    Hello @hwesley,

    As @pedmec said. “uA Low ck FRod” = microamp Low check Flame Rod. Or the flame has an issue and has poor contact with the Flame Rod.

    Also it appears the unit retains some fault history.
    You may find the manual interesting.

    https://carlincombustion.com/wp-content/uploads/MN60200FR1-070319-Instructions-web-2.pdf
    National - U.S. Gas Boiler 45+ Years Old
    Steam 300 SQ. FT. - EDR 347
    One Pipe System
  • Steamhead
    Steamhead Member Posts: 17,334
    This is on a Carlin EZ-Gas burner, right?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • mattmia2
    mattmia2 Member Posts: 10,783
    What were the combustion reports from these companies that worked on it?