Watching the pressure drop during a long heating cycle.
Hap_Hazzard
Member Posts: 2,846
So, we had a cold morning today, so I fired up my boiler for the first time this season so I could check for leaks. The house was about 65 degrees, so I set the thermostat to 70 and let it run for about a half hour, keeping an eye on the pressure gauge.
Once the main vents closed, the pressure shot up to 0.5 psi and stayed there for a while. Then, as the radiators filled, the pressure gradually decreased. By the end of the cycle, the pressure had dropped to about 0.05.
Once the main vents closed, the pressure shot up to 0.5 psi and stayed there for a while. Then, as the radiators filled, the pressure gradually decreased. By the end of the cycle, the pressure had dropped to about 0.05.
This surprised me. I guess I’ve never sat and watched it this long before. I had assumed that, after reaching 0.5 psi, the pressure would stay about the same or maybe increase as the radiator vents closed, but, apparently, as the radiators fill with steam, they start condensing it faster than the boiler can generate it. Am I right about this? And if that’s the case, would I be correct in concluding that the EDR of the radiation (including piping) is a little higher than the output of the boiler?
Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
0
Comments
-
It sounds like your boiler capacity and radiation are perfectly matched. Did the house heat evenly?—
Bburd0 -
could be a little under but as long as you have pressure (some at the far end) it will be fine. Just need enough to distribute the steam evenly0
-
bburd said:It sounds like your boiler capacity and radiation are perfectly matched. Did the house heat evenly?Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
You can fine tune the distribution by adjusting the radiator vents. Your system should run efficiently and well.—
Bburd0 -
bburd said:You can fine tune the distribution by adjusting the radiator vents. Your system should run efficiently and well.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Hello @Hap_Hazzard,
Seems normal to me, when the Main vent closes less overall venting, higher pressure. The higher pressure persists until the Horizontal Run-Outs and the Risers warmed up. (this is why pipe insulation is so important to minimize the reheating of the pipes every cycle). I'm betting your radiator vents did not close before the thermostat was satisfied (or you shut the test down early) since you did not see the pressure rise near the end of the cycle. If you want to see the pressure rise near the end of the cycle you probably need a recovery from a deeper setback or the outdoor temperatures need to be much closer to design day temperatures. Especially if your boiler and EDR are well matched.Hap_Hazzard said:Once the main vents closed, the pressure shot up to 0.5 psi and stayed there for a while. Then, as the radiators filled, the pressure gradually decreased. By the end of the cycle, the pressure had dropped to about 0.05.
This surprised me. I guess I’ve never sat and watched it this long before. I had assumed that, after reaching 0.5 psi, the pressure would stay about the same or maybe increase as the radiator vents closed
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
To me, it sounds like your radiator venting is lacking
The reason being, it's building up to 1/2 a pound to get the steam into the radiators. Once they start condensing the pressure drops to something more reasonable.
Under the same conditions here's what I've observed many times. This is what the system runs at with everything cold. I started recording as the main vents were closing.
https://youtu.be/zyxLbXq61-U
Now, if the radiators are fairly warm or even hot like when it's in the single digits out I have seen it climb up a little and then drop down, repeatedly. Up to 0.75" and back down to 0.5" for example.
The reason yours is getting to 1/2 a pound is your holding the steam back more than you need to. Let the system breath.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
ChrisJ said:To me, it sounds like your radiator venting is lacking The reason being, it's building up to 1/2 a pound to get the steam into the radiators. Once they start condensing the pressure drops to something more reasonable. Under the same conditions here's what I've observed many times. This is what the system runs at with everything cold. I started recording as the main vents were closing. https://youtu.be/zyxLbXq61-U Now, if the radiators are fairly warm or even hot like when it's in the single digits out I have seen it climb up a little and then drop down, repeatedly. Up to 0.75" and back down to 0.5" for example. The reason yours is getting to 1/2 a pound is your holding the steam back more than you need to. Let the system breath.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-241 -
I’m using all the available vent sizes, from #4 to D, so I can’t increase the venting without screwing up the balance.Hap_Hazzard said:ChrisJ said:To me, it sounds like your radiator venting is lacking
The reason being, it's building up to 1/2 a pound to get the steam into the radiators. Once they start condensing the pressure drops to something more reasonable.
Under the same conditions here's what I've observed many times. This is what the system runs at with everything cold. I started recording as the main vents were closing.
https://youtu.be/zyxLbXq61-U
Now, if the radiators are fairly warm or even hot like when it's in the single digits out I have seen it climb up a little and then drop down, repeatedly. Up to 0.75" and back down to 0.5" for example.
The reason yours is getting to 1/2 a pound is your holding the steam back more than you need to. Let the system breath.
That's good to hear.
So you're not running all Hoffman 40's or Gorton 4's like some.
I suppose it is what it is. your system wants that little bump to get things moving and then it drops down.
Do you hear any noise from any vents during that or do they all remain fairly quiet?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
They’re Maid-o-Mist, bimetal type vents, so they’re silent unless they get condensation in them, but that won’t happen until it gets colder.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements