Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Medium pressure to low presssure ductwork
kmann44
Member Posts: 1
Does anyone have experience with medium pressure ductwork
I was looking a existing job with medium and low pressure dw. They have pneumatic air valves to reduce duct pressure in office zones
i was wondering if a vac box can do the same thing as the pneumatic valve
it is a pressure dependent arrangement
i was wondering if a vac box can do the same thing as the pneumatic valve
it is a pressure dependent arrangement
0
Comments
-
If you're talking about a VAV .......variable air volume system yes, the supply medium pressure duct from the air handler is generally run with about 1" of static pressure which feeds VAV boxes. In the old day the boxes were pneumatically controlled now they use DDC controls0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements