Crown Bimini BWC225 Error Code E03
ChucksOldBoiler
Member Posts: 14
in Gas Heating
My Gas fired Crown Bimini BWC225.
It's only 12 years old and now reads error code E03
I replaced the ignition electrode & cable.
Also cleaned the heat exchanger which was very clogged.
Still has error code E03. Any ideas?
It's only 12 years old and now reads error code E03
I replaced the ignition electrode & cable.
Also cleaned the heat exchanger which was very clogged.
Still has error code E03. Any ideas?
0
Comments
-
@ChucksOldBoiler ,
I'm wondering why you "I replaced the ignition electrode & cable." ? Cleaning the Heat Exchanger probably would not have hurt, but may not have gotten you any closer to the E03 situations remedy.
Using the manual found here;
https://www.velocityboilerworks.com/documents/bimini_150_225_installation_manual.pdf
Table 13.4: Hard Lockout Codes Displayed (Manual page 53, PDF page 55)
E 03 - Gas valve error
• Loose or defective gas valve harness. Check electrical connections.
• Defective gas valve (check for 24 VDC at harness during trial for ignition before replacing valve)
Once the condition that caused the lockout is corrected, the boiler will need to be manually reset using the RESET button on the display.
I assume you tried the reset.
" The BWC boiler uses a microprocessor based control, known as a “MCBA ”
Apparently the MCBA has a Supervisory or Monitoring capability so it thinks there is a problem with the Gas Valve or the Gas Valve's circuit or wiring harness. I would pursue that direction.
National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System1 -
You can try removing the wire connector from the gas valve and replacing it. This small procedure can "clean" the contact between the plug and the pins to improve the electrical connection.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
The gas valve is defective.
Thanks for all your help guys.
Case closed
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements