Is there an insert/seal missing in this brass circulator?
JackW
Member Posts: 236
Comments
-
-
Yes, there should be a gasket between the motor and volute where they join. It usually sticks to the motor. Check for a very thin black gasket.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
@Alan (California Radiant) Forbes I didn't see anything when I took the circ apart, but I'll check. As I noted to hot-rod, the stators plastic impeller is different than the older ones. There is a gasket between the stator and pump housing, but that's not what I'm asking about; I'm asking about the machined recess in the middle of the housing. Thanks for your input.
0 -
-
I think he is referring to the wear ring you see in the volute hole in some circs. I see them mainly in high head circs where the hole in the eye of the impeller is smaller and needs to match the hole in the volute, generally a closed type impeller
That being an open impeller the water can get to the canes across that large volute hole
I think😗Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
@hot_rod, ahh, good to know. I emailed the seller, and he said it came that way in the box from the company. So I trust him, and thanks for your input. I've replaced the three cast-iron circs with brass ones, plus replaced all the ferrous parts with non-ferrous parts, I have everything soldered up, with a few changes required, so I should be good to go. Appreciate all your help.
Thanks,0 -
@Alan (California Radiant) Forbes, hot_rod said the same thing, plus I checked with the seller, and he said it came that way from the company. Thanks for your help.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements