Viega Manifold Actuator Wires
Alan (California Radiant) Forbes
Member Posts: 4,214
I was trying to fit two actuator wires into one terminal of a Taco zone valve control and noticed that the end switch wires fit easily, but it was a struggle to get two of the 24 volt wires to go in until I noticed they were a different gauge. Surely, the smaller gauge would be adequate for both?
The red wires are end switch.
Max Inrush Current: 300 mA for 2 minutes maximum
Operating Power: 1W
Micro Switch: 24VAC/0.5A
The red wires are end switch.
Max Inrush Current: 300 mA for 2 minutes maximum
Operating Power: 1W
Micro Switch: 24VAC/0.5A
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
This is maybe a long shot, but maybe they engineered it that way to discourage the way you were trying to hook it up. I've seen two different gauge wires under a screw head without an pressure equalizing plate causing an intermittent connection to the smaller diameter wire. Do you have a picture of what you were trying to do?National - U.S. Gas Boiler 45+ Years Old
Steam 300 SQ. FT. - EDR 347
One Pipe System0 -
Are the ends of the wires crimped? If you strip it back it little and get the stranded wire. Twist it and slide them in.
0 -
that's how the get you to install there brand across the board. bet it fits easily into there control0
-
Maybe cut the crimp ferrules off the ends, they make the wire a bit larger.
Plenty of room under the Caleffi connections, high and low voltage terminals😉
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I like the crimp ferrules because stranded wire gets frizzy and hard to handle when you miss the opening; easy for this far-sighted plumber. It can also splay and short out on a neighboring wire. I ended up ganging the wires with a wire nut and running a single wire to the control.
@109A_5 Sorry, I didn't take a picture.
I was just curious why the manufacturer would go to such trouble; if there's a reason. Perhaps an electrical code requirement?8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
I've been told that ferrules or soldered ends are code, on stranded wire, in European markets? I bought a ferrule kit at one of the Euro trade shows, it is a handy tool to own for the reasons you mentioned.
The lower right ferrules accept two wires for a single connection.
www.ferrulesdirect.com has kits and tools.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I always thought you were a feral kind of guy.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Stranded wire under a pressure plate if it is small wire like 16, 18, 14 etc I will strip it long and fold it back over itself to get a little more "meat"0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements