How much more head would a buffer tank (water heater) add ?
Dave Carpentier
Dave Carpentier Member Posts: 640
edited May 2022 in THE MAIN WALL
I plotted a boiler's head against the curves of my Grundfos UPS pump. How much more head would be presented when adding a buffer tank with a half dozen 1" 90's and squeeze it thru the 3/4" tank openings of a side-port water heater (a 12 gallon "tall" water heater used as buffer) ?
Edit.. adding graph
  • Larry Weingarten
    Larry Weingarten Member Posts: 4,184
    Hi, What sort of GPM are you looking at? Better would be to share the system curve so we can see the fuller picture. My old System Syzer gives me about 3.5 GPM for 3/4" type L copper, so you would be turning over the volume of the tank in about three and a half minutes... if than helps! :p
    Yours, Larry
    hot_rod Member Posts: 28,062
    Idronics 16 walks you through the steps to plot a system curve. Everything in that circuit needs to enter into the calculation. EL, equivalent length of fittings and devices
    Then lay the system curve over the pump curve to determine the OP, operating point, which is where the two curves cross
    STEVEusaPA
  • Dave Carpentier
    Okay. All 1".. I imagined 7 elbows, 2 sideport tees (the "generous pipes" attached to the buffer), a coupla reducers, 2 ball valves, 10' of pipe, and a little glycol at 130f pushed at 7gpm. Ran it thru the formula and got 1.5ft of additional head.
    If I add 1.5ft to the pump-vs-boiler curve intersection (on medium speed), that now puts me potentially below the max heating side flow out of the tank. So now I bump the speed up on my 3-speed pump and recalculate using the pump-vs-boiler intersection (on high speed). The new calculation gives me 3 ft of head (in addition to the boiler at that flow speed), and I end up with 7gpm.
    Hopefully that ballparks it.
    15-42 is an older model Grundfos, the 15-58 is a newer 3 speed model, the boiler you are considering has a 15-42?
     15-58 or some have a 15-62 OEM version on mod cons
  • Dave Carpentier
    The Lochinvar Epic (non-combi) needs a field-supplied boiler circ. The 15-42 is my 20 yr old. Lived the first 10yrs on high speed as my secondary circ , then 10 yrs as my primary circ at low speed.
    Should I consider replacing it due to mileage ?
    No noise from it, but that's a pretty good amount of spin time I suppose.
    Retire it and keep as a emerg backup (it could replace either of my Boiler or System circs in a pinch) ?
    The UPS15-58 looks like an exact match, if I need one. Thanks.
    Run em till they drop, replace with ECM  style for less power consumption, torquier motor, digital display, when the time comes