Proper 1" NPT connections
Steve Garson_2
Member Posts: 712
I am installing a new circulator and need some guidance on how many threads beyond hand tight should a 1" copper NPT fitting screw into a cast iron flange.
Thanks!
Steve
Thanks!
Steve
Steve from Denver, CO
0
Comments
-
-
The last few times I used them I had bad luck with copper male NPT adapters, the threads were terrible.
When making an NPT connection you want to tighten it until you feel the threads bind. Basically, it'll gradually get tighter and tighter, but feel smooth and linear. And then, all at once it'll feel like it gets really tight fast, that's the spot you want to be in, in general.
I'd highly recommend using a few wraps of good PTFE tape like Blue Monster followed by a coating of pipe dope over the tape. Try to push / thread the tape into the threads with your fingernail after you do all of the wraps and then put the pipe dope on.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
That's a tough question to answer. The threads vary so much from product to product. Hand tight, maybe two turns. Often over-tightening is as much as a problem. Teflon tape and dope tends to allow over torquing the connection. A 12" wrench or pliers should be plenty for a 1" threaded connection.
Those iron flanges tend to be painted on the threads also, further complicating the joint.
A sweat flange, or sweat Webstone iso valve smooths out the connection assembly from copper to pump flangeBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
To quote a favorite mentor, " it depends ". Condition of the fitting and male / female threads matter, and, the size of pipe wrenches, pliers, arms, work space, and experience all matter, too.
The more modern flanges have a better tool grip area with square shoulders for better leverage.
I agree with others regarding tape & dope, but in some cases we'll start with string or ball wicking, then 3 /4 wraps of quality Teflon on top; making sure each is back a thread or two from the end. A light coating of quality pipe dope brushed on clockwise along with the string & tape finishes the assembly prep - 2 or 3 full turns beyond hand tight is usually enough.
0 -
My first answer is to tighten it enough so it don't leak, but not to tight to crack it.
BUT I have the best answer. FA-GET-A-BAT-IT! and Use 'Dis
no need for threads or dope or tape or nothin'
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
i've had enough bad experiences with copper to iron transitions that I'd use a brass sweat to thread or a Webstone fitting like Ed shows.Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0
-
I have had copper chilled and hot water coils where the MFG brazed female adapters on the coil stub. Dumb.
Of course, brazing annealed the female adapter and softened it. When we cranked a male adapter into it it bottomed out before it got tight.
I took it back apart and cut 2 threads off the male adapter re-doped it and it was ok, but I didn't like it.
I could probably un-brazed the female adapter on the coil, but the stubs were short. Wanted to exhaust the other options.
Luckly, it didn't leak, my next step was going to be taking the male adapter out and cleaning off the dope & tape and screwing it back in and brazing the two adapters together, but I didn't have to.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements