Question about panel radiator installation
55Trucker
Member Posts: 20
Hi, I installed three Ecostyle wall panel radiators that I purchased from Ecomfort.com. I finally got everything hooked up today and turned on the heat. The installation guide is a little light on detail, specifically, I was led to believe that the supply and return lines at the bottom of the radiator could be reversed. I did find more detail in the install guide I found for another brand, which looks identical to what I bought. That install guide seems to imply that you must connect the radiator this way:
Two of the radiators are the same size (16"w x 36"h). The third one is bigger, 36"w x 16"h.
One of the two 16" radiators is plumbed the reverse of this flow diagram, but both get hot.
The larger (36" wide) radiator is plumbed reverse and only gets hot on the right third of it. Note that the flow control valve on the radiator (that can accept a thermostatic control, but I don't have one) is set to 6, which should mean it's wide open.
Can reversing the supply/return cause what I am seeing?
Two of the radiators are the same size (16"w x 36"h). The third one is bigger, 36"w x 16"h.
One of the two 16" radiators is plumbed the reverse of this flow diagram, but both get hot.
The larger (36" wide) radiator is plumbed reverse and only gets hot on the right third of it. Note that the flow control valve on the radiator (that can accept a thermostatic control, but I don't have one) is set to 6, which should mean it's wide open.
Can reversing the supply/return cause what I am seeing?
0
Comments
-
Inside pipe is always the supply. May not work well. reduced flow at best.
0 -
You probably have air in some of those riser tubes, did you power purge it with pressure?
Water should flow either direction, but if you add TRVs the flow direction needs to be correct.
Sometimes flowing backwards thru a bib type valve pushes the sealing washer off and it may not flow.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
-
yes, when they referred to reverse connections they meant the supply and return are on the total opposite side of the radiator but the supply is always the inside tapping. not reversing the existing supply and return tapping. correctly installed piping first per manufacturers specs. then proceed0
-
Perhaps you can reverse the piping under the floor so it can't be seen?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements