Flue temperatures too low?
Mrubens
Member Posts: 3
in Gas Heating
I have a natural gas boiler and have recently had issues with condensation in my chimney. Part of the issue is the chimney is unlined (I will be getting a liner).
However, I had a service person out and they measured a flue temp (at the exhaust port) of 280f and said this could be contributing to the condensation. They like to see 310-320F.
My question is, is it possible to increase the exhaust/flue temperature on a boiler?
However, I had a service person out and they measured a flue temp (at the exhaust port) of 280f and said this could be contributing to the condensation. They like to see 310-320F.
My question is, is it possible to increase the exhaust/flue temperature on a boiler?
0
Comments
-
I bet the gas input is too low. But don't try to fix this yourself! You need a pro with proper test equipment.
Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thanks. I'm in New York, capital region
Wouldn't try to fix it myself just looking to see if this is an issue that an HVAC tech can fix by fiddling with the boiler or if it's a sign that it's on its way out.0 -
0
-
EBEBRATT-Ed said:What @Steamhead said. What is your return water temp? Is this a converted gravity system?
It is a gravity system I think. There is no recirculation pump. (old boiler, services 2nd floor only)0 -
The condensation is a result of the low stack temperature. a Liner may help increase the temperature because it will heat up faster and draft better. More draft will pull flue gas thru the boiler a bit faster. Gravity heating lends itself to lower return temperature for longer time period.
Did this boiler heat the first and second floor in the past? I ask this because I remember the first time I split a boiler that did a 4 unit apartment building into 4 separate boilers. I used the existing oil boiler to heat the hardest zone to repipe. (which was not the largest zone BTW). Then disconnected and capped off all the other radiator connections.
Then I purchased 3 small gas boilers and 3 gas water heaters and connected the individual zones to separate boilers on different gas meters. This left the old oil boiler way oversized for the apartment zone. (after 3 years the landlord purchased the final small gas boiler because he couldn't keep a tenant in the Oil Heat apartment.). Either pay now or pay later
If your current gravity boiler did the entire building in the past, then it is way oversized. Is it possible that someone derated the boiler to a lower input in order to lower operating cost? Not such a good idea! If so, than a smaller boiler is in order.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements