Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
NTI Trinity Ti 200 - er3
PDM
Member Posts: 4
Last year I had er3 (Water Probe – The Sentry is sensing an open circuit at the water probe. Or, the outdoor or water probe circuit is grounding). The outdoor probe and terminals were dry. I replaced the Thermistor and its wire harness and the boiler has worked until last week. The old thermistor checked out fine by the way. I attached the wire harness to the old thermistor (just hanging in air) and then warmed it up a little - it was enough to get the boiler going and once the water started to get warm I shut the boiler off, put the wire harness back on the installed thermistor and its running okay without issue. I can order another Thermistor but as the old one didn't seem to be bad I'm wondering if I need to be looking elsewhere. I appreciate any insights.
0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 97 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 929 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements