Radiant controlling Triangle Tube Solo boiler output temp
Eja55
Member Posts: 2
Have a Triangle Tube Prestige Solo 110 piped p/s. Two circuits on panel radiators, one on radiant floor, one DHW. Install 12 years ago with no issues on operations. ODR installed. Recently a problem has developed concerning the supply water temp. When the floor is operating the water temp is around 100-110, when the panels are operating at the same time the temp stays at low temp. Shut off the radiant floor, temp goes up to 160 as required. Have a Apollo 34A mixing valve for the radiant floor circuit. All pumps seem to be working. This issue just started this year. Thinking possible failed mixing valve. Looking for some direction..
With the floor only calling for heat and then watching as a call for heat is made for panel rad zone, if the boiler temp doesn't increase appropriately, I would think something is wrong with the boiler. I wouldn't suspect the mixing valve if the floor is heating as desired. Call to Triangle Tube tech support?0
Where are the thermostats landed? What is controlling the circulators? Are the circs coming from the boiler? And all 3 zones TT going to the boiler?
If so, then there is most deinatly a glitch in the boiler logic.Serving Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
The heating stats are all connected to a Taco switch relay,. DHW stat is on the indirect Smart connected directly to boiler control. The more I watch the boiler operation, I noticed when call for DHW, supply only goes to about 140-150, when it should be 180+. Have another control module, will change it.
This boiler has been flawless in operation for 12 years, so I should expect some issues to start showing up.0
- 87.5K THE MAIN WALL
- 119 Geothermal
- 394 Solar
- 15.9K Strictly Steam
- 50 Industry Classes
