Stiebel Eltron recirculation pump Model No. CP3S15-62FC
My problem seems to be the pump. It is installed correctly and is about 12" above the water level. I cannot get the pump to prime and continuously pump my water.
Question: Does this pump require head pressure to work? Will it not draw water up twelve inches once primed?
Has a built-in check valve which seems useless in a system that would require head pressure?
If I am using the wrong pump what brand and model do you recommend? I don't need a bunch of system this and that. I simply need a pump that will move 5-15 gpm.
Thanks.
Comments
-
Pump or circulator ? Looks like a Grunfos circulator .. Which is not a self priming pump , it creates a pressure drop to move water . Why a open system ?
There was an error rendering this rich post.
0 -
Move the pump below the water level. Outdoor wood furnaces always have the pump at the bottom of the tank, they are also open systems
Or stick a high temperature sump pump in the tank😉Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
ty bob. I was wondering if gravity feed was enough.
0 -
The old gravity systems worked because of the large diameter piping. The hotter water would rise up in the large pipes that had very low flow resistance, cooler water would fall down. Systems that are piped with 3/4, 1 , 1-1/4" sized piping generally need a circulator to cause the flow to move. It provides the energy to move the fluid.
The typical small wet rotor circulator needs about 4 psi pressure at temperatures around 180- 190F. placing the pump as low in the system as possible should provide enough pressure to keep the pump working properly. A. centrifugal type circulator will not lift water out of an open container.
The water will stay in the piping above an open boiler as long as you do not have any auto air vents up high point.
It is possible at high temperatures to pull a vacuum in the system, if you have piping a story or so above the water level, running 180F or lower should be fine.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
It is not installed correctly- as Bob mentioned, it needs to be below the water level. Lower equals more head pressure which is better.0
-
I moved the pump down near the floor and piped it. There is about 2' of standing water above it. Pump comes on but still doesn't move anything.
So I have two 1" lines running to the basement. One feeds hot water and the other returns it. They attach to six valve manifolds that segregate my zones.
I am looking for a different pump. Ideally I'd like a 12v recirculation pump. 3-6 gpm.
Anyone have any suggestions.0 -
Did you purge the air out of the circuit and all the loops? if there is an air bubble that pump, any pump, will not circulate.Csmith1967 said:I moved the pump down near the floor and piped it. There is about 2' of standing water above it. Pump comes on but still doesn't move anything.
So I have two 1" lines running to the basement. One feeds hot water and the other returns it. They attach to six valve manifolds that segregate my zones.
I am looking for a different pump. Ideally I'd like a 12v recirculation pump. 3-6 gpm.
Anyone have any suggestions.
B&G has a 12VDC Eco Circ, but it is a fairly small, low performance circBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Im not familiar with B&G. What company is that.
Yes on purging. The pump was below the water level and filled with water when I opened the valve. It just will not pump any water.0 -
3 things you need to know to select a circulator
fluid type
gallons per minute
head or pressure loss of the circuit
Here is the Bell & Gossett eco 12VDC it will do 3 gpm or so, depending on the pressure drop.
As for pressure on the pump, if there is water at the suction and discharge, regardless of a check valve, then the distance of the water above the circulator is the pressure on it. If your water level is two feet above, you have 2' head. It is seeing the pressure from the suction side if there is a check at the discharge
A few reasons that it is not circulating
air lock
not spinning, jammed rotor, installed backwards
a closed valve somewhere, obstruction in the piping, are all the manifold ports open??
sized too small to overcome the head, or pressure drop, doubtful
disconnect a loop at the manifold, see if it is circulating that far, or take a short piece of pex and jumper from a supply to return.
Those pumps with internal checks sometimes get air locked right in the pump body. Loosen the flange bolts on the discharge side to burp that air bubble.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Im getting surgery this week then off to Mayo for ten days so not going to do much more.
Brand new pump. Actually, have two.
I ran a 5' line from bottom of boiler tank to the pump that was below the tank then a 6' line back into the top of the tank. An 11' open circuit with pump below water level and not pushing any pressure. Still nothing.
No valves or obstructions.
The steibel eltron is the recommended pump. I let the water gravity from the tank through the pump then plugged it in. Starts and hums, but it doesn't move water. The pump is turning. I'm baffled.
I order a 12v self-priming 3.1 gpm pump I will hook to our battery bank with wind/solar When I am back.
ty all for the help.0 -
-
As Groundup mentioned, it is all but impossible for the circulator to not cause the water to move.Csmith1967 said:Im getting surgery this week then off to Mayo for ten days so not going to do much more.
Brand new pump. Actually, have two.
I ran a 5' line from bottom of boiler tank to the pump that was below the tank then a 6' line back into the top of the tank. An 11' open circuit with pump below water level and not pushing any pressure. Still nothing.
No valves or obstructions.
The steibel eltron is the recommended pump. I let the water gravity from the tank through the pump then plugged it in. Starts and hums, but it doesn't move water. The pump is turning. I'm baffled.
I order a 12v self-priming 3.1 gpm pump I will hook to our battery bank with wind/solar When I am back.
ty all for the help.
Assuming it is installed properly, arrow pointing the correct way
Sized properly, sounds like it is
No obstructions in the pump or piping
Is the impeller spinning or just the motor? It fairly easy to break the ceramic shaft in those circs, if they are dropped, for instance.
Remove the 4 allen bolts and confirm it is spinning, or look in the end on the bench when powered up.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
I will definitely check that Bob, ty.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements