Taco Viridian Circulator Pump Light Is Blinking - Why?
Kman18
Member Posts: 14
While the pump is on, it will sometime blink 5 times....what does this mean?
0
Comments
-
These circulators have an auto-correction feature built in.
When running, if the light starts to flash white and then back to normal color, then you may have an air issue. This circ will recognize if there is air present in the volute of the circ, it is trying to purge the air by quickly slowing down then speeding back up to normal. I have also seen this occur when your system pressure is low and you have a failed (or almost failed) expansion tank and the relief valve has operated.
The other auto-correction feature has a red and white light flash. This in indicative of a rotor not rotating freely. This is telling us to take a look at the water quality for any solids and/or black iron oxides in the water. If this is the instance, the circ will stop, quickly jog the rotor back and forth and then go back to high speed trying to rid whatever is holding or impeding the rotor from spinning freely.
The air purge function will occur indefinitely whereas the locked rotor function will occur for 20 minutes and then stop altogether and you will end up with a red light.
Here is a video to see the function and the lights
Dave H.
Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
1 -
Thanks. The light on my pump is blue only, it was installed about 7 years ago.0
-
You may not see the quick change of the LED to white from blue.
Dave Holdorf
Technical Training Manager - East
Taco Comfort Solutions
0 -
Nope, It's blue only.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements