Just had a mid-winter "no heat" call where everything seemed to be operational except possibly oil delivery. Priming revealed a large amount of air purging required before reestablishing a fire.
The customer's oil tanks had a 3/4 filled active and a totally empty, valved lockout in parallel to the filter.
Despite the recent single tank fill it appears that the second tank lockout valve was leaking, allowing the system to ingest air under successive lowered head pressure fill conditions to eventual prime failure.
Tightened both ball-valve stem packings to hopefully alleviate, but will suggest to customer that they either operate with both tanks self-leveling or leave some fuel in the empty to improve sealing.
The customer's oil tanks had a 3/4 filled active and a totally empty, valved lockout in parallel to the filter.
Despite the recent single tank fill it appears that the second tank lockout valve was leaking, allowing the system to ingest air under successive lowered head pressure fill conditions to eventual prime failure.
Tightened both ball-valve stem packings to hopefully alleviate, but will suggest to customer that they either operate with both tanks self-leveling or leave some fuel in the empty to improve sealing.
0
Comments
-
If the 2nd tank isn't used anymore, why not take it out of the run.
If you power purged the oil line, with an oil watcher or clear tubing on your vacuum gauge, you would see if there is any air ingress. Could also be a vacuum leak from a valve, fitting, filter, pump cover or flare.There was an error rendering this rich post.
0 -
I would think an inactive tank is jut a cause of a potential problem. I would use it or remove it0
-
Is the oil supply lines and call equalizing lines to the burner top feed ?
There was an error rendering this rich post.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements