weil Mclain wm97
creger.robert
Member Posts: 40
in Gas Heating
wm97 high effeciency boiler natural gas-burner fires for 12 seconds then shuts down and go thru cycle again and again-never goes to a code on screen-gas pressure is good.
check vent and intake open-any thoughts
check vent and intake open-any thoughts
0
Comments
-
Is this a WM-97-155? If so, check the burner gasket. The gasket is conductive and part of the flame rectification circuit. If it is compromised you will get a weak flame signal and the problem that you have described. You can also try reconfiguring the control to a model 110 which allows for a lower flame signal. If it runs in this configuration you will want to check the burner gasket.1
-
I had and solved the same issue with my WM97+ 155 boiler.r
Enter the contractor setting menu ( up and down together for 7 sec ) and go to diagnostics, manual test mode.
Keep an eye on the "flame signal"
If a flame signal of > 160 is not obtained in 5 seconds it will cycle again.
I have the same boiler and agree it could be the burner gasket issue. But it could also be a dirty ignitor or a damaged ignitor gasket. Take the ignitor out and clean with a scotch pad, also make sure the ignitor gasket is in good condition.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements