Gas pipe addition question

davehosler
davehosler Member Posts: 4
Looking to add a gas dryer on the far side of my house. Will use black pipe. When I got my permit back, the inspector added a note where I indicated that I was going to tap into the existing pipe that says “tie in as per 2018 IFGC”. I’m connecting a 1” black pipe into an existing 1.25” black pipe. I was going to use a 1.25” T with 2 - 1” connections (one for the existing appliance run, the other for the new pipe run). Would that satisfy code? Thanks

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    IFGC is reffering to the "international fuel gas code"

    Can't say for sure without a sketch of the piping and the loads connected.

    But why would you run 1" to a gas dryer? Gas dryers are usually around 35,000 btus 35cfh of gas/hour.

    You would seldom have to run anything larger than 3/4" to a dryer maybe even 1/2" if the run isn't too long.

    Be better if you post a sketch
  • davehosler
    davehosler Member Posts: 4
    Went through all the required sizing with the town. Can’t say for sure why the 1” is required but not a problem, just trying to figure out if there is anything specific needed to “ tie in as per 2018 IFGC” that is more than a properly sized T. Thanks
  • delcrossv
    delcrossv Member Posts: 1,344
    Proper support of runs, proper use of drips, dope, not tape etc.

    Here's the code:

    https://codes.iccsafe.org/content/IFGC2018/chapter-3-general-regulations
    Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.
  • davehosler
    davehosler Member Posts: 4
    Thanks, didn’t know if I was missing something. Seems straight forward.
  • mattmia2
    mattmia2 Member Posts: 10,952
    According to the table in the code, 3/8" iron pipe is good for 22,000 htu/hr at 150 ft, so half inch is probably sufficient unless your house is like 300 ft.
  • davehosler
    davehosler Member Posts: 4
    All of my sizing was fine for all of the appliances existing and proposed. The only thing that made me question my ability was when my permits came back with a specific notation “tie in as per 2018 IFGC” where I was going to tie in. I questioned myself as to why they felt the need to add that note as I had thought I was doing everything to code and assumed I missed something. I guess I just over though it.