Gas pipe addition question
davehosler
Member Posts: 4
in Gas Heating
Looking to add a gas dryer on the far side of my house. Will use black pipe. When I got my permit back, the inspector added a note where I indicated that I was going to tap into the existing pipe that says “tie in as per 2018 IFGC”. I’m connecting a 1” black pipe into an existing 1.25” black pipe. I was going to use a 1.25” T with 2 - 1” connections (one for the existing appliance run, the other for the new pipe run). Would that satisfy code? Thanks
0
Comments
-
IFGC is reffering to the "international fuel gas code"
Can't say for sure without a sketch of the piping and the loads connected.
But why would you run 1" to a gas dryer? Gas dryers are usually around 35,000 btus 35cfh of gas/hour.
You would seldom have to run anything larger than 3/4" to a dryer maybe even 1/2" if the run isn't too long.
Be better if you post a sketch0 -
Went through all the required sizing with the town. Can’t say for sure why the 1” is required but not a problem, just trying to figure out if there is anything specific needed to “ tie in as per 2018 IFGC” that is more than a properly sized T. Thanks0
-
Proper support of runs, proper use of drips, dope, not tape etc.
Here's the code:
https://codes.iccsafe.org/content/IFGC2018/chapter-3-general-regulationsTrying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.0 -
Thanks, didn’t know if I was missing something. Seems straight forward.0
-
According to the table in the code, 3/8" iron pipe is good for 22,000 htu/hr at 150 ft, so half inch is probably sufficient unless your house is like 300 ft.0
-
All of my sizing was fine for all of the appliances existing and proposed. The only thing that made me question my ability was when my permits came back with a specific notation “tie in as per 2018 IFGC” where I was going to tie in. I questioned myself as to why they felt the need to add that note as I had thought I was doing everything to code and assumed I missed something. I guess I just over though it.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements