Topic Update :: return>supply, pictures added
Macaroni12
Member Posts: 9
Update: I think my issue has to do with zone 3 driving up return temp, or supply sensor in wrong location. Pictures and more detail below. You guys are very helpful. Thank you
Hi all - New homeowner here with a Weil Maclean Ultra 155 Boiler System (3 zone) -- Home was struggling to stay >62 degrees on days <20 degrees outside - Turns out circulator pumps were not zoned properly. That was adjusted and home has been much warmer, however today was the 1st true test and the first floor was floundering around 65 degrees this morning- Has since warmed up as the temp increased outdoors.
The house is raised ~7ft off the ground (exterior foundation walls are not insulated, ceiling of crawlspace is) and the boiler pipes run across the ceiling outside of the insulation. They're however, currently wrapped in foam pipe insulation -- Suspect that those pipes are losing quite a bit of heat when the temp drops below 20 -- Short of insulating the whole walk in crawlspace, would better fiberglass insulation help? Raising the water temp on cold days?... Or is none of this an issue and i'm back at square on of boiler setup, which I realize required quite a bit more information .. Just trying to get a sense of if it could be a meaningful variable.
Appreciate your guidance.
Hi all - New homeowner here with a Weil Maclean Ultra 155 Boiler System (3 zone) -- Home was struggling to stay >62 degrees on days <20 degrees outside - Turns out circulator pumps were not zoned properly. That was adjusted and home has been much warmer, however today was the 1st true test and the first floor was floundering around 65 degrees this morning- Has since warmed up as the temp increased outdoors.
The house is raised ~7ft off the ground (exterior foundation walls are not insulated, ceiling of crawlspace is) and the boiler pipes run across the ceiling outside of the insulation. They're however, currently wrapped in foam pipe insulation -- Suspect that those pipes are losing quite a bit of heat when the temp drops below 20 -- Short of insulating the whole walk in crawlspace, would better fiberglass insulation help? Raising the water temp on cold days?... Or is none of this an issue and i'm back at square on of boiler setup, which I realize required quite a bit more information .. Just trying to get a sense of if it could be a meaningful variable.
Appreciate your guidance.
0
Comments
-
Hi, Insulation is rarely applied so the heat loss is negligible. Best would be if you could have a look at the lines with an IR camera, so you could clearly see if and where the heat is escaping. Depending on the temperatures involved, you might be able to use polyethylene, rubber, or fiberglass insulation. I've even put two layers of foam insulation on some piping, staggering the seams, to be certain of greatly reduced heat loss. Pay special attention to any air leaks at insulation joints or seams. Hope that helps!
Yours, Larry0 -
What is the supply water temperature at the boiler? Do the controls adjust that temperature based on the outdoor air temperature (outdoor reset, or ODR)?—
Bburd0 -
supply temp is dropping below 150 when all 3 zones are on and I get a return>supply error when only 1 zone is on.I’m back to thinking it’s a settings issue. ~20 degrees today and can’t get the whole house above 67.
Boiler seems to default to priority 3 no matter how many zones are calling for heat. Priority 3 = circulator pump 2. Ignores pump 1 and 3
priority zone 1= all 3 circulator pumps
Priority zone 2= pump 2 and 31 -
Make sure it’s not a vented crawl which is typical if the walls aren’t insulated and the floor above is.Personally I’d insulate and seal the exterior walls and create a conditioned space. You’ll find the space above become much more comfortable and any loss from the radiator pipes will remain in the home.0
-
here’s some photos of the setup which I suspect will help. Much appreciate ld
0 -
I have a tankless heater.I don’t know if at a point there was a DHW zone hooked up to this. I just bought the house
4 zone switching relay, though only 1-3 seem active.
i just raised min on time for priority 3, given that seems to be driving all 3 zones (including my primary)
zones 2+3 are OK temp wise, though zone 3 not perfect and zone 1 is currently 61 degrees (set to 70)
seems like zone 1 doesn’t have its own primary? Trying to figure out how to debug primary setting zone by zone
thank you for your guidance so far0 -
Update. After another night of low teens high single digit
zone 1 is now 57
zone 2 is now 66
zone 3 is now 66
this thing is locking itself out every 10-15 minutes stating return temp higher than supply
oddly as I stared at the boiler from 1-4 am, the supply temp never drops below the return temp on the he screen. Just on the diagnostics screen
to recap, boiler only seems to be using priority 3 for a 3 zone system. At this point I have circulator pump 2,3 on and reduced flow to 75. Can’t seem to do anything to avoid return above supply lockout0 -
I think my return and supply sensors are swapped.
the “on screen” is showing proper supply of ~150 and return of ~130
And at the exact time of lockout, the lockout diagnostics screen shows supply of ~130 and return of ~115
could someone help me confirm this? Seems to jive but not sure
Really appreciated from helpless new homeowner
0 -
To follow up, I figured out how to follow the sensor wire to the connection. It looks wired properly
it seems zone 1 will run completely fine if alone, adding zone 2 doesn’t bring an issue. As soon as zone 3 is added my return temp jumps
Supply temp sensor location is right after the split for the 2nd zone. Should it be just after the supply outlet before any split. In theory would think this is a higher reading that could keep up with higher supply?
or I guess the real question is why is zone 3 driving up my return temp
zone 1 is first floor radiator
zone 2 is second floor baseboard (except master)
zone 3 is finished attic baseboard and master
temp sensor pic below
0 -
Alright. I just ‘nudged’ the sensor in its current location to see if it was a contact issue. Supply temp immediately shot up ~40 degrees and is in line with boiler output.You have got to be kidding me…0
-
Take some more pictures from farther back. Pump #1 looks like the boiler pump unless it's piped wrong0
-
Thanks. Better? Are the green circulators the “pumps” or just zone control? If so I’d think all three should be on?Currently running on pump 2 for what that’s worth..0
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements