Oversized flue liner: min vs max BTU
HomeownerDustin
Member Posts: 28
I need my flue liner replaced for 4 gas appliances (2-unit home) with max total output 264k BTU/hour.
The long-term plan is to take over both units and just run 1 set of appliances.
If we did that, we could potentially just close up flue liner rather than resize it, and bring all the hydronics + hw to a single mod/con and indirect. Any thoughts on whether to convert the 45 year old boiler to a mod-con now are also appreciated.
House stats:
Edit: just to be clear, I have no intention of putting mod con through the flue. If I take 1 units appliances out of the flue by getting a mod con, then the flue would use a 5” liner. If I don’t take 2 appliances out, I need a 7” liner.
- Current liner diameter is 5" on a 30' run, and the liner doesn't go to the top of the chimney (didn't know when we bought).
- Correct liner diameter is 7" for these 4 appliances at max 264k BTU ([https://lifetimechimneysupply.com/chimney-btu-calculator/2-or-more-category-1-appliances/get-liner-diameter.php](https://lifetimechimneysupply.com/chimney-btu-calculator/2-or-more-category-1-appliances/get-liner-diameter.php))
- We're debating replacing one boiler (45 years old) and DWH tank with a modcon plus indirect HW tank, so max output up the flue would be 132,000 BTU on the remaining 2 appliances, which corresponds to a 5” liner. The boiler that would remain is 20 years old right now (Burnham series 2).
The long-term plan is to take over both units and just run 1 set of appliances.
If we did that, we could potentially just close up flue liner rather than resize it, and bring all the hydronics + hw to a single mod/con and indirect. Any thoughts on whether to convert the 45 year old boiler to a mod-con now are also appreciated.
House stats:
- 125 years old 2-family home, very leaky, balloon framed. We're hopefully getting insulation put in by next winter (contingent on renter getting energy assessment done).
- Unit 1
- 45 years old boiler that burns 100k BTU, heating capacity 78k BTU (78% eff)
- HW is 32k BTU
- monoflow with old fin tube convectors
- Unit 1 heat loss is 33.5k BTU/hr, determined empirically with heat bills per GBA.
- 45 years old boiler that burns 100k BTU, heating capacity 78k BTU (78% eff)
- Unit 2
- 20 year old boiler that burns 96K BTU, heating capacity 80k BTU (83.3% eff)
- HW is 36k BTU
- monoflow with mix of old fin tube convectors and baseboard fin.
- unknown heatloss but probably around 40-45k BTU. Based on my unit's heat loss + they have the poorly insulated roof and bigger place.
- 20 year old boiler that burns 96K BTU, heating capacity 80k BTU (83.3% eff)
Edit: just to be clear, I have no intention of putting mod con through the flue. If I take 1 units appliances out of the flue by getting a mod con, then the flue would use a 5” liner. If I don’t take 2 appliances out, I need a 7” liner.
0
Comments
-
-
The liner must be listed to UL 1738 for CAT IV venting under positive vent pressure with a modcon. There were one or two ss listed so listed but I'm not sure if they're still around. Find out the make and alloy of the liner.0
-
-
STEVEusaPA said:Why would you vent a mod con into the flue when you can direct vent with pipe thru the wall.
I’m not. Mod con would direct vent, so I’d only have 132k btu up the flue vs current 264 btu.0 -
Bob Harper said:The liner must be listed to UL 1738 for CAT IV venting under positive vent pressure with a modcon. There were one or two ss listed so listed but I'm not sure if they're still around. Find out the make and alloy of the liner.0
-
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements