Utilizing circulator hold off with hydrolevel 3250 and taco zone valve control

super_snop
Member Posts: 48

0
Comments
-
If the zone valve fails to open, technically (almost always) the end switch won't close, and T-T won't make
There was an error rendering this rich post.
0 -
And as Steve said above, the circ will also not turn on.
On a ZVC controller, the sequence of operation is:
1. Thermostat Call
2. Power to zone valve
3. End switch on zone valve closes
4. XX (isolated end switch) closes and XX (pump end switch) closes
Take out the end switch on the zone valve and the boiler nor the circ turns on.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco, Inc
0 -
Thanks guys. I was under the impression that if there was a call for heat from thermostat XX would close and the end switch for the pump would only close after the zone valve end switch makes. Looks like I can wire the circ through the hydrolevel and still be able to utilize hold off function without worrying about pumping with a closed zone valve.1
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements