Utilizing circulator hold off with hydrolevel 3250 and taco zone valve control

super_snop
Member Posts: 48

0
Comments
-
If the zone valve fails to open, technically (almost always) the end switch won't close, and T-T won't makesteve0
-
And as Steve said above, the circ will also not turn on.
On a ZVC controller, the sequence of operation is:
1. Thermostat Call
2. Power to zone valve
3. End switch on zone valve closes
4. XX (isolated end switch) closes and XX (pump end switch) closes
Take out the end switch on the zone valve and the boiler nor the circ turns on.
Dave H.Dave H0 -
Thanks guys. I was under the impression that if there was a call for heat from thermostat XX would close and the end switch for the pump would only close after the zone valve end switch makes. Looks like I can wire the circ through the hydrolevel and still be able to utilize hold off function without worrying about pumping with a closed zone valve.1