Honeywell aquastat setting help

jpetrarca4
jpetrarca4 Member Posts: 2
Hi guys, I’ve been having some issues. First off I’m in the northeast, I have oil heat with baseboards and a tankless coil for water. I’m trying to adjust my aquastat so my family doesn’t run out of hot water when showering. It happens more in the winter when the heats on. Right now I have the high at 195, low at 175 and diff is set to 15 or 20.   Any help would be great on which one I should be changing. I’ve read the low but I’m not sure if I should raise it or lower it. Thanks again 

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 3,020
    You are pushing it at your settings now. Did you try cleaning the coil ? A storage tank would be recommended ....

    There was an error rendering this rich post.

  • jpetrarca4
    jpetrarca4 Member Posts: 2
    I haven’t cleaned the coils. I’ll have to research that and see if it’s a diy thing. Also I’ve read to put diff to 25. If I do that should I lower the low setting? Or still leave it 20 off the high setting?
  • SuperTech
    SuperTech Member Posts: 2,430
    Descaling the tankless coil may help, bit it won't completely solve the problem.  A storage tank or an indirect water heater would be a better setup, but the least expensive way to make the hot water temperature consistent would be to install a thermostatic mixing valve on the coil. This will regulate the temperature of the water and help extend the time it takes for the coil to cool down. 
  • Big Ed_4
    Big Ed_4 Member Posts: 3,020
    edited January 2022
    Try to bounce the coil . Run full hot water though a "bath tub" and quickly shut off the valve before or after the coil . Sometimes you can get the coil to bounce and shake loose the solids ..

    There was an error rendering this rich post.

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Typical situation where with the deeper freeze, colder incoming water is entering the coil, so less dhw production.

    There was an error rendering this rich post.

    SuperTech