Suzy
Suzy Member Posts: 4

Good morning, I am so glad I found this forum. Our tank ran dry (long story). After it was filled, I bled the burner and cranked it up…until it stopped again after about an hour. I changed the nozzle, wool filter by the tank, and screening filter in the burner (Beckett AFG). They weren’t too dirty. Problem is, I cannot get the burner to bleed now. I push the reset button, but when the blower comes on, I get only air coming out of the bleeder valve.  I’ve reset it several times. Any thoughts? What else should I troubleshoot? Also, there isn’t diesel pooling in the furnace at this point, right? 

PS:  My furnace guy is coming Monday, but only for a quick look. We live in a very remote area, and he’s really, really busy. 

Comments

  • Big Ed_4
    Big Ed_4 Member Posts: 2,785
    edited January 2022
    Options
    Changed the filter cartage at the tank ? Is the tank bottom feed ? If so did you bleed the filter using the bleeder on top of filter first ? Your not loading up the unit with oil , until the pump is pumping oil ...

    There was an error rendering this rich post.

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    If you ran out of oil you probably clogged the oil line. SOP is to remove filter element from canister/replace canister, put a push/pull pump at the burner, blow the line back into the tank, replace filter element, re-bleed the line.
    Is it a gravity system (gravity from tank to burner), or a lift system (burner above tank)?

    There was an error rendering this rich post.

  • Suzy
    Suzy Member Posts: 4
    Options
    Thank you, Big Ed_4 and STEVEusaPA. My system must be a lift system. The tank is outside, and the lines go underground, under the crawlspace, and through the floor to the furnace.
    I think I installed the filter at the tank incorrectly--I did not bleed the filter first. I'll try that. If that doesn't work, I'll blow the line back into the tank as Steve suggested.
  • Steamhead
    Steamhead Member Posts: 16,856
    Options
    "Lines"? As in, there are two pipes between the burner and the tank?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,546
    Options
    @Suzy

    are you sure you opened any valves in the system? Check that anything you took aapart is properly connected and tight
  • HVACNUT
    HVACNUT Member Posts: 5,841
    edited January 2022
    Options
    Some pics would help a lot.
    How do you plan on blowing back the line?
  • Suzy
    Suzy Member Posts: 4
    edited January 2022
    Options




    Here are photos of the lines from the tank, and into the burner. The tank is about 6 months old; the furnace is from 2008 (and ran great until the "empty tank incident"), and the lines are probably original to the house, in 1966. It is usually chilly here, but almost never gets below freezing.
    I Googled "push-pull pump" and I have one in the workshop. I'll use that, as suggested by Steve, after I double check my completed work.
  • rick in Alaska
    rick in Alaska Member Posts: 1,457
    Options
    I would check to make sure the pieces you took apart are all sealed up ok, especially if you are getting air. You might want to take the filter back apart and pour some oil in to it to give things a little help getting going. Also, if everything is air tight, then all you should have to do is just fire up the burner and it should self bleed. Assuming the bypass plug is installed.
    Rick
  • HVACNUT
    HVACNUT Member Posts: 5,841
    edited January 2022
    Options
    Have the tech install a Firomatic valve at the burner. 
    Robert O'Brien
  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    Options
    Oil filters should be installed indoors only
    To learn more about this professional, click here to visit their ad in Find A Contractor.
    kcoppHVACNUT
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,546
    Options
    theop says it almost never gets below freezing i don't see an issue wit the outside filter.

    My concern would be the old steel/galvanized lines run underground if they are 55 years old.
    bucksnort
  • rick in Alaska
    rick in Alaska Member Posts: 1,457
    Options
    Oil filters should be indoors because it helps warm the oil, but there are a million of them outside, and it does work. If you are worrying about freezing, then make sure there is not water in the tank.
    Rick
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    Holy s#*!

    There was an error rendering this rich post.

    Suzybucksnort
  • Suzy
    Suzy Member Posts: 4
    Options
    Thank you everybody, it's working now! I added oil to the filter, and tightened the cover to the strainer. That did the trick.
    Now I'll look into the bypass plug and Firomatic valve. Hopefully the technician can spend some time with the furnace in a month or so.