Viega Hydronic Mixing block kicks off heat mode after just a few minutes.
johntlukens
Member Posts: 2
Having trouble with my Viega Hydronic mixing block's controller. It turns red for heat for only a few minutes then kicks off. Replaced the TPC sensor, no change. Disconnected thermostat, no change. Help!
The manual is attached.
Looks like you can bypass the thermostat by jumping terminals 1 & 2 on the mixing block in most cases. Read the manual before trying this.
Make sure it is plugged into a working 120 volt outlet
Check the wiring connections for the thermostat and the two sensors.
You could have a bad sensor. You have a boiler temp sensor on the boiler and an outdoor temp sensor.
To check the sensors disconnect them from the mixing block and ohm them out with an ohm meter. Take the outdoor air temp and the boiler temp with a thermometer and compare the ohm readings you get with the chart Page 19 I think.
If the ohm readings don't agree you may have a bad sensor
Also read the programming instructions and see if the sensor temps are reading on the screen1 -
Thank you! I have tried all of your suggestions with no luck. A new question: If I choose "constant" in the menu of choices, will the mixer just run?0
It looks like in constant it will run all the time if the outdoor sensor is telling it to. You would need to go through the manual0
- 125 Chimneys & Flues