Caleffi 553 Autofill-New install on existing system-Not working
hcpatel78
Member Posts: 154
Hi,
I have the radiant system installed last year with a Noritz Combi boiler. The Noritz autofill does not work somehow so I installed a new Caleffi autofill 553.
After completing install and turning on the water supply still the valve is not able to fill and pressurize the system at all. My system is still at 10 psi. I set the fill pressure at 20 at autofill still it is not able to fill and pressurize the system.
Am I doing something wrong?
I have the radiant system installed last year with a Noritz Combi boiler. The Noritz autofill does not work somehow so I installed a new Caleffi autofill 553.
After completing install and turning on the water supply still the valve is not able to fill and pressurize the system at all. My system is still at 10 psi. I set the fill pressure at 20 at autofill still it is not able to fill and pressurize the system.
Am I doing something wrong?
Thank you,
Hiren Patel
Hiren Patel
0
Comments
-
What is your incoming city/well water pressure? It doesn't appear you have a water line connected to the Caleffi0
-
It is connected while I posted. Some pictures I took during work were going on. Upon further investigation found out that the backflow preventer installed before autofill is not letting pass any water through somehow.
Strange!
I am on well and supply pressure is 40-60 psi at the inlet on the backflow preventer.
Brand new install last year and never check that part. Initially, I filled my system with a purge valve so never had a chance to look that was it working or not?
Is it ok to remove the backflow preventer as the Caleffi autofill 553 has included a check valve in it?
Thank you,
Hiren Patel0 -
The gray knob on the bottom, it’s a shutoff is it open?
Yes the fill valve does have an outlet check, but it doesn’t meet code as A BFD. It will stop reverse flow as it is a spring check.
Does pressure increase as the screw in top is turned? Sometimes the gauge doesn’t match the setting number
BFD is flowing the correct direction?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes. That gray knob is open. The backflow preventer is culprit. It is installed in correct direction. But somehow stuck . It looks like it was bad from beginning .
Can I install caleffi backflow preventer (standalone one) vertically?
I would like to replace this bad one with caleffi one if I can install vertically.Thank you,
Hiren Patel0 -
Thank you all. Found a problem. Back flow preventer is bad. I would like to replace with better one like callefi or so.Thank you,
Hiren Patel0 -
If it is a vented dual check, here is what most all brands look like inside. Basically two spring checks. One must be stuck? You might split it open and clean it out. if the rubber parts are stiff or cracked or glued together, best to replace.
With the check in the Caleffi AutoFill you will be fine until you replace the BFD. Or just shut off the fill valve for 100% backflow protection
Yes the 573 can be installed vertically with the vent port down. The reason being if it does discharge all the water needs to drain out of the vent. If the port is up, water sits inside and corrodes the seals. And the vent port should be piped to the floor also.
Requirement enforcement varies widely on boiler BFDs. In one state 3 different types are allowed by various jurisdictions. Dual check, dual check with vent port, and RPZ type. It can come down to the actual inspector's opinion.
For your own use, if it is plain water in the boiler I feel the vented dual check is adequate. Best protection is the RPZ, but by code those must be tested and re-certified yearly $$.
If you use the Caleffi assembly BFD and AutoFill you actually have 3 check protection, that should handle it
I'd use a RPZ for peace of mind if you have non-potable chemicals in the boiler.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
👍 thank you so much Bob,
Hiren.
Thank you,
Hiren Patel0 -
Problem solved. Caleffi water feeder is working the way it is supposed to be and filled and pressurize my system at 14-15 PSI.
Thank you all for your quick help. You guys are awesome.
Regards,
Hiren PatelThank you,
Hiren Patel0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements