Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Steam trap & vents
Snowmelt
Member Posts: 1,425
I installed a boiler , old one was shot …….. it has both main vents steam vents and traps….. someone on a Facebook page said one or the other ? Also the same one with a condensation pump
0
Comments
-
Two pipe or one pipe?
One pipe is vents, two pipe is usually traps..............usually.
But it depends on what type of system it is and how it's piped
There is a two pipe air vent system for instance
And depending on the system and how it's piped you could have a trap on a one pipe system especially with a condensate pump
And you could have part of a two pipe system that needs air vents if the returns drop into a wet return.
There are a lot of usuals but no hard and fast rules0 -
Pics!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements