Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Steam trap & vents

Options
Snowmelt
Snowmelt Member Posts: 1,416
I installed a boiler , old one was shot …….. it has both main vents steam vents and traps….. someone on a Facebook page said one or the other ? Also the same one with a condensation pump

Comments

  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,568
    Options
    Two pipe or one pipe?

    One pipe is vents, two pipe is usually traps..............usually.

    But it depends on what type of system it is and how it's piped

    There is a two pipe air vent system for instance

    And depending on the system and how it's piped you could have a trap on a one pipe system especially with a condensate pump

    And you could have part of a two pipe system that needs air vents if the returns drop into a wet return.

    There are a lot of usuals but no hard and fast rules
  • Steamhead
    Steamhead Member Posts: 16,867
    Options
    Pics!
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting