Steam trap & vents
Snowmelt
Member Posts: 1,425
I installed a boiler , old one was shot …….. it has both main vents steam vents and traps….. someone on a Facebook page said one or the other ? Also the same one with a condensation pump
0
Comments
-
Two pipe or one pipe?
One pipe is vents, two pipe is usually traps..............usually.
But it depends on what type of system it is and how it's piped
There is a two pipe air vent system for instance
And depending on the system and how it's piped you could have a trap on a one pipe system especially with a condensate pump
And you could have part of a two pipe system that needs air vents if the returns drop into a wet return.
There are a lot of usuals but no hard and fast rules0 -
Pics!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0