Many boiler water levels

dopey27177
Member Posts: 916
Taken from my book Steam the Perfect Fluid for Heating




Jake




Jake
Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron
by Jacob (Jake) Myron
1
Comments
-
3 techs looked at one of my MIL's boilers that was constantly overfilling off a VXT autofeeder- including two probe replacements.
None of them considered flipping the dip switches adjusting the delay in feeding to account for a sluggish condensate return. It's amazing the difference 6 minutes makes. 😉👍Trying to squeeze the best out of a Weil-McLain JB-5 running a 1912 1 pipe system.1 -
Thanks @dopey271770
-
Steam: The Perfect Fluid for Heating and Some of the Problems
by Jacob (Jake) Myron0