Goodman furnace issues
Comments
-
When was the last time it operated properly?
https://www.theacoutlet.com/documents/Owners-Manual-Goodman-GPG13.pdf This is the manual. Service starts on page 33.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Look at the wiring that is connected to the new control board. See if there are any wires that are burnt or have melted insulation. Look where the wires may get close to the flame
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I was looking at the sequence of operation on page 24. it appears that at about the time you describe the control board blows a fuse, there is a change from the high to the low flame operation. This is an indication that the low speed fan may be blowing the fuse. Look at the wires to the Induced draft blower (the small fan near the exhaust outlet) to see if there is any damage to that wiring
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
I noticed It not working when I woke up in the middle of the night Sunday when my ecobee thermostat told me that the furnace had ran for 3 hours straight and the house temp had dropped 3 degrees. When I get home in the am, I will check the wires coming out of the inductor fan, and all of the wires that are around that area. I know there is a metal hole like 1” in diameter that the wires for the inductor fan, flame sensor, igniter, limit switch, and gas valve go through that is bare metal.0
-
That should have a wire connector clamp or a grommet so the wires can't rub and chafe the insulation away.nismogsxr said:I noticed It not working when I woke up in the middle of the night Sunday when my ecobee thermostat told me that the furnace had ran for 3 hours straight and the house temp had dropped 3 degrees. When I get home in the am, I will check the wires coming out of the inductor fan, and all of the wires that are around that area. I know there is a metal hole like 1” in diameter that the wires for the inductor fan, flame sensor, igniter, limit switch, and gas valve go through that is bare metal.
Poor workmanship, especially if that is the cause of the problem.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Didn’t see anything wrong with any of the wires. Looking at where I thought was wires going through a ole that was bare metal, there was a grommet there. It had fallen out, so I put it back in place. Testing for a short I noticed that of the two wires for the furnace limit switch, one side has continuity to ground. That wire goes to the propane valve, which then goes to the contactor. From that terminal on the contactor, it goes to the transformer where it’s on a terminal that goes to a ground. So I guess that is ok for having continuity to ground lol. But when looking at my contactor I also noticed some black and melting. I have continuity on both poles of the switch without pushing the contactor in. I am just wondering if that contactor is my whole problem. I know it needs to be replaced, but praying that’s my issue0
-
Is there a gap between the poles of the contactor? It looks like it is welded together but it is hard to tell from that angle.0
-
Sometimes I have seen in really cheap appliances where they just hem the edge of the metal and hope it doesn't cut through the wiring.EdTheHeaterMan said:
That should have a wire connector clamp or a grommet so the wires can't rub and chafe the insulation away.nismogsxr said:I noticed It not working when I woke up in the middle of the night Sunday when my ecobee thermostat told me that the furnace had ran for 3 hours straight and the house temp had dropped 3 degrees. When I get home in the am, I will check the wires coming out of the inductor fan, and all of the wires that are around that area. I know there is a metal hole like 1” in diameter that the wires for the inductor fan, flame sensor, igniter, limit switch, and gas valve go through that is bare metal.
Poor workmanship, especially if that is the cause of the problem.1 -
Sometimes I have seen in really cheap appliances where they just hem the edge of the metal and hope it doesn't cut through the wiring.mattmia2 said:
That should have a wire connector clamp or a grommet so the wires can't rub and chafe the insulation away.
Poor workmanship, especially if that is the cause of the problem.
OP found the grommet and put it back. I have seen that also Matt
@nismogsxr
The picture shows a 220V contactor that should be replaced. That operates the compressor. It has nothing to do with the heating system or the low voltage fuse on the PC board. You need to find where the overload or short circuit is in the 24 Volt Control circuit. That fuse is there if more than 3 amps (or 5 amps) goes thru the 24V control system. That is usually caused by a thermostat wire. (I'm guessing the green one but can't be sure. I'm not MacGyver trying to disarm a bomb here.)
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
There is a gap there, but there is continuity on both sides of the switch without pushing contactor innismogsxr said:mattmia2 said:Is there a gap between the poles of the contactor? It looks like it is welded together but it is hard to tell from that angle.
That continuity may be from the wires going thru the compressor and the other electrical devices on the system. To truly check continuity, you must remove the wires.
With the electricity turned on, see if there is a difference of voltage between the black wire connection and the white wire connection, with the wires connected. If there is voltage, then the contactor is open and not the cause of the low voltage fuse failure.
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements