Boiler setting for panel radiators?
skiereric
Member Posts: 66
I am questioning the boiler setting (as well as most things with my system) for my Weil-Mclain 155 97+.
My house is heated by 25 Stelrad panel radiators + one beacon morris kick space heater.
I have realized the heat setting is currently set to "Fan-coil" which has a preset max supply of 190 and min supply of 140.
As well as Boiler Circulator Spd of High, Min run time is set to 15 minutes.
I don't think a Stelrad panel is a "fan-coil" I believe the max supply is too high for my Stelrad panels.
Any advice on what the boiler heat setting should be for this setup? I have attached the manual, page 77 is the relevant page.
My house is heated by 25 Stelrad panel radiators + one beacon morris kick space heater.
I have realized the heat setting is currently set to "Fan-coil" which has a preset max supply of 190 and min supply of 140.
As well as Boiler Circulator Spd of High, Min run time is set to 15 minutes.
I don't think a Stelrad panel is a "fan-coil" I believe the max supply is too high for my Stelrad panels.
Any advice on what the boiler heat setting should be for this setup? I have attached the manual, page 77 is the relevant page.
0
Comments
-
Were the Stellrad radiators designed for 180 SWT or 140SWT ? Your existing settings are too high and will need to be reduced. The amount of reduction is directly related to the sizing of the Stellrads. I design for 140 and the radiators are larger, but heat the home at design temp on the coldest days. I presume the radiators were installed with thermostatic radiator valves?
0 -
You're right on track: The fan coil setting is too high.
Go with the CIB (Cast Iron Baseboard) settings; it should keep you plenty warm.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Out of the 25 rads, 12 have TRVs (however all are without a head - I am picking up heads today) 8 have shut off valves and the remaining have no control at all.Paul Pollets said:Were the Stellrad radiators designed for 180 SWT or 140SWT ? Your existing settings are too high and will need to be reduced. The amount of reduction is directly related to the sizing of the Stellrads. I design for 140 and the radiators are larger, but heat the home at design temp on the coldest days. I presume the radiators were installed with thermostatic radiator valves?
0 -
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements