Need some insight on a Riello Gas burner please.
Riello 40 N200S conversion burner. Installed on a Buderus G2154 boiler. i installed this 6 years ago and it has been flawless.
In the last few weeks it has started acting up. It will lock out at random times.
Typically a Saturday morning customer wakes to no heat at 6am.
It resets w/o issue each time.
I started off looking at the gas pressure. Static is anywhere from 7.19" wc to 8.53"wc
under load it drops to 6.07"wc
I replaced the primary and found a ground wire that was not connected.
All was great for a week.... Then this Saturday and again today it locked out.
Of course I start and stop the burner several times and it runs fine.
Any ideas where to start looking next?
TIA.
    EdTheHeaterMan Member Posts: 12,506
    I am not sure how Riello proves the gas flame for safe operation, but if it is like so many others, there is a flame rectification circuit. See if the flame sensor electrode or flame sensing rod needs to be cleaned or replaced.
    kcopp