Connecting Taco Controls and Nest Thermostats

HeatingHelp.com
Member, Moderator, Administrator Posts: 135
Here are instruction sheets for Nest to Taco ZVC with 3-wire application, Nest to Taco ZVC with 2-wire application, Nest to Taco SR with 3-wire application, and Nest to Taco SR with 2-wire application.
Forum Moderator
0
Comments
-
Erin and all,
We have also spoken with Nest recently in regards to wiring and they suggest using the resistor wiring as shown but they do suggest using a 220 ohm, 5 watt resistor instead of the 1,000 ohm, 0.5 watt resistor we supply with the controllers.
Dave H.Dave Holdorf
Technical Training Manager - East
Taco, Inc
1 -
Also make sure to pre-charge the Nest so that the battery is at 100% before wiring to the ZVC or SR controls.0
-
-
Do the Taco ZVCs apply power to close the valves, or are they assumed to be self-closing? Said differently, does the Nest connect power from Rh to W1and C respectively when calling and not calling for heat?0
-
Is there a similar instruction sheet for Nest to Taco XPB-1 with 2-wire application?
Many thanks!
0
Categories
- All Categories
- 86.8K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 106 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 104 Geothermal
- 160 Indoor-Air Quality
- 3.6K Oil Heating
- 69 Pipe Deterioration
- 954 Plumbing
- 6.3K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements