Taco SR503-4 relay
heavenlyheating
Member Posts: 4
My question is, I installed the taco sr503-4 switching relay. The jumper that goes between ZC and ZR, do I have to install the jumper between those two terminals?
0
Comments
-
So I walked into WindowRama, went up to a bay window, and asked the sales rep "Will this fit in my wall?"
Sorry.
What model aquastat do you have? If it's "cold start", then yes, the jumper gets installed. If the boiler has a tankless coil, then ZR,ZC on the relay should get wired to ZR,ZC on the aquastat.
Did you have 3 separate switching relays and upgraded?
Gas, oil, mod con? There are reasons you might want to delay the start of the circulators.2 -
it’s a taco SR503 switching relay, it had two separate relays and I installed the taco relay. I will install the jumper and see if that helps. Thanks for the advice0
-
Sometimes, even Heavenly People just can't take a joke!
Or understand about the window of Sarcasm.
Or answer the simple question about what aquastat is on their boiler.
I hope the jumper works!
Good Luck and Happy Thanksgiving.
If it does not, then bring back more information Mr. HH
Yours Truly,
Mr. EdEdward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements