Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Bosch Greenstar floor mount combi P151 (kwb42-3) boiler pressure
pwoll
Member Posts: 2
I have a Bosch Greenstar fs combi kwb42-3 boiler with a pressure gauge that is resting
less than 1 bar and need to top up the pressure to 1 bar. Need to know how to top up
the pressure. I cannot find and key or keyless valves in the unit.
less than 1 bar and need to top up the pressure to 1 bar. Need to know how to top up
the pressure. I cannot find and key or keyless valves in the unit.
0
Comments
-
1 bar is 15 psi so that is plenty.
Post a few pictures.
There must be a city water make up pipe feeding the boiler with a pressure reducing valve on it.
Unless you have antifreeze in the system?0 -
Ed
Yes there is a city water make up pipe feeding the boiler with a auto fill (green) valve on it. No other
valves after the auto fill valve. That the problem. See attached pics. Any ideas?
0 -
Take a close up pic of that valve on your last picture. See what the numbers say on the tagAnyway that’s the domestic water (or) plumbing, nothing to do with the 1 Bar dial0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements