Gorton main vent venting steam

Options
Don_175
Don_175 Member Posts: 126
We have a relatively new Gorton vent on a branch in our basement. It is about 6-8” above the pipe on a pipe nipple and is releasing steam when the heat is on. Is there any way to clean it etc? They seem to be pretty expensive. Thanks 

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,737
    Options
    I would contact Gorton, they have excellent customer service and would most likely replace it.  If it’s new it shouldn’t be dirty already and it shouldn’t vent steam.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,523
    Options
    @Don_175

    Do you know if you are running high steam pressure? High pressure kills vents. Should keep it below 2 psi lower is better
  • Don_175
    Don_175 Member Posts: 126
    Options
    No. Pressure is definitely low. .5 psi