I have a steam radiator that does not get hot and when I look to open the supply valve I noticed there isn’t one. Does one need to be installed or can I open without one? 

Comments

  • neilc
    neilc Member Posts: 2,854
    edited November 2021
    your first picture is the valve, missing its handle,
    it (the handle) may have broken, or been removed to prevent tampering,
    post a picture of the other end of the radiator,
    is there a second pipe there?(2 pipe system) or any little vent devices about half way up?(1 pipe system)
    that answer will prompt better advise on the valve you're questioning,
    pliers on that top disc, rocked gently back and forth, may get you some movement,
    counterclockwise is more open, clockwise = closed,
    if system is 1 pipe, valve should be all the way open, and you would control the heat at the vent,
    that pipe thru the wall, and radiator should pitch back to the valve, (far end higher than the valve end)
    if system is 2 pipe, valve can be throttled,

    known to beat dead horses
  • JUGHNE
    JUGHNE Member Posts: 11,279
    Are these pictures of the same radiator?
    Can you get a picture with more light, showing both ends?
  • PC7060
    PC7060 Member Posts: 1,445
    JUGHNE said:
    Are these pictures of the same radiator? Can you get a picture with more light, showing both ends?
    Looks like same pipe viewed from
    opposite sides of wall penetration 
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,485
    good eyes @PC7060
    PC7060