Hey all. This is my first post. Disclaimer:
I’m a commercial reno / service plumber just got into residential service the past year. Not much heating experience. A family friend asked me for help with a brand new boiler problem. They got a Utica mgb 095 installed and were getting no heat to the baseboards. The feed and the return were both getting hot and one baseboard would start to get warm.  Original plumber or handyman whatever he is couldn’t figure it out. I called customer support and explained everything. They had the air scoop and then the circulator pump on the return. The tech told me this was the problem, the air scoop needed to be on the feed. So I followed his advice and re piped the air scoop. Fired up the boiler and everything worked great. So now I know what the problem was, but I want to know why. Why did this matter? Why would that make such a difference? I know this was long. Thanks for reading!

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,262
    Look for a book called "Pumping Away" by Dan Holohan, the founder of this website.

    The first install was probably air bound in the BB heaters.
    The second install would have removed the air easier and quicker.
    Rich_49
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 16,295
    What @JUGHNE said,
    It should have worked either way but "pumping away" is the better choice
    PC7060