feed water

Options
steam247
steam247 Member Posts: 12
why do we sometime put the feed water line at the compression tank on hot water boiler and others with a feed water/ cut-off combination. i understand by the tank is the place of no pressure change.  looking to understand why we sometimes don’t put it at the tank and put a combination feeder/cut-off instead off return.

Comments

  • PC7060
    PC7060 Member Posts: 1,160
    Options
    @638Jay - “looking to understand why we sometimes don’t put it at the tank and put a combination feeder/cut-off instead off return.”

    I’m not tracking, do you have an picture or drawing of this configuration?
  • neilc
    neilc Member Posts: 2,703
    Options
    because sometimes the manual doesn't get read
    known to beat dead horses
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,546
    Options
    @638Jay

    You want the feeder (pressure reducing valve) and expansion tan to "see" the same pressure. The air pressure in the expansion tank and the feeder pressure should match.

    Other than that I have seen many jobs where the feeder is connected in a different location and it works fine as long as there is no appreciable pressure drop between the ex tank and feeder it will be fine.

    Example:Putting the expansion tank on one side of the circ pump and the feeder on the other would be a bad thing
  • steam247
    steam247 Member Posts: 12
    Options

  • steam247
    steam247 Member Posts: 12
    Options
    the top pic has feed water at tank and bottom pic has a combination feed water/ LWCO . looking to understand why and when. most books say to have it at tank “ point of no pressure change”  . but i see it also the other way 
  • EBEBRATT-Ed
    EBEBRATT-Ed Member Posts: 15,546
    Options
    @638Jay

    Like I said in my first post. It dosen't matter. As long as the expansion tank and the PRV feeder are seeing the same pressure it's fine

    In the bottom picture they are feeding water into the bottom of the boiler and the expansion tank is connected to the top of the boiler

    With a cast iron or steel boiler they are basically like a big tank full of water.

    There is negligiable pressure drop between the two points so it's fine

    If we were talking about a mod con boiler it would be different

    Connecting the tank together with the water make up is always a good thing to do. Just because someone did it differently doesnt mean it's wrong
  • steam247
    steam247 Member Posts: 12
    Options
    thank you , yea depending what page you are on in a text book lol. most book say put feed water on line that connects the tank. but when you get to the page on LWCO it shows it this way and never explains why it’s different.