Burnham LE Oil fired boiler long turbulator no longer available

scraphound
scraphound Member Posts: 7
We're planning to service four Burnham LE series oil fired boilers and I'm guessing some turbulators will need replacing. Burnham no longer makes the long turbulators the boilers came with. Is it ok to replace only the damaged ones with the new shorter turbulators and re-use the long ones that are good, or do we need to replace them all?

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Sure, give it a whirl. But make sure you check & set your draft properly. I'd probably mix and match short and long so that all the longs aren't in one section and the shorts in the other.