I'm soliciting opinions on this Laars Mini-Therm boiler. I like the idea of having my guys easily carry 200,000 BTUs down rickety old Brooklyn cellar steps rather than risk injury with a 500-pound piece of cast iron as they have for decades.
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Laars-JX200NLIU1-Brochure.pdf
I'm soliciting opinions on this Laars Mini-Therm boiler. I like the idea of having my guys easily carry 200,000 BTUs down rickety old Brooklyn cellar steps rather than risk injury with a 500-pound piece of cast iron as they have for decades.
https://s3.amazonaws.com/s3.supplyhouse.com/product_files/Laars-JX200NLIU1-Brochure.pdf
Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes
0
Comments
-
One would think they would have included the shipping weights in the spec sheet.
Certainly less than standard CI.0 -
Flow I think is the key to keeping them happy. Primary Secondary. They get a lot of use in pool heaters etc.
I bet @Alan (California Radiant) Forbes see's a lot of these2 -
What Ed said about proper flow rate. They work best on primary/secondary. Year ago, I did some work for them. I asked their engineers if they ever considered making a steam boiler. He said they had one now. "All you have to do is use the wrong pump," he said.
Pipe it right (as I know you will) and I think you'll like these a lot. And your point about the rickety Brooklyn stairs would sure be my convincer.Retired and loving it.0 -
I would add that they like a consistent load as they are usually a fixed output. Some models had two stage gas valves.
On a multi zoned system, especially with micro zones a buffer may be desired.
They need boiler return protection if used on low temperature radiant.
Hard to beat copper as a heat exchange material, these have a long proven history and are fairly bulletproof even in abused installations These and other copper tube brands were the go to in the early radiant days.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Agree with all the above. I service about 200 or more of them here in the Bay Area; their JVS Mini-Therms were very popular in the 80's and 90's and are still going strong; almost indestructible. They will soot up when they serve radiant unprotected, so 1°-2° piping is in order.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
The delta T pump across the low loss header is cool. The literature mentions adjustable water temperature and outdoor reset. I guess the control PWM's the gas valve?0
-
Thanks, Dan. Every time we lug a cast iron hot water boiler into a house I shake my head and wonder how long we're going to do this for.DanHolohan said:
Pipe it right (as I know you will) and I think you'll like these a lot. And your point about the rickety Brooklyn stairs would sure be my convincer.Contact John "JohnNY" Cataneo, NYC Master Plumber, Lic 1784
Consulting & Troubleshooting
Heating in NYC or NJ.
Classes0
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 95 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements