Boiler air baffle
mjstraw
Member Posts: 41
Burnam Holiday boiler from mid-70's (?) with internal air separating baffle piped to steel compression tank. Works well - I've only had to drain the tank twice in 20 years.
Getting ready to add second zone using an additional circulator. @DanHolohan's "Piping Away" book says boiler baffles don't work well with multiple circs.
I could add an air separator piped to the tank, or switch to a bladder tank and air elimination. But I envision a large bubble of air trapped behind the baffle from when only one circ is running.
Will this be a problem?
Getting ready to add second zone using an additional circulator. @DanHolohan's "Piping Away" book says boiler baffles don't work well with multiple circs.
I could add an air separator piped to the tank, or switch to a bladder tank and air elimination. But I envision a large bubble of air trapped behind the baffle from when only one circ is running.
Will this be a problem?
Mark
Indiana PA
Indiana PA
0
Comments
-
What pages refer to this situation?0
-
Page 57Mark
Indiana PA0 -
So then your system would look like page 59, with circs instead of zone valves.
I have never dealt with this situation; IDK....someone else here later in the day may respond.
Is your old tank original from the 70's? 45-50 years old.
Bladder tank will not last that long.
FIWM, I would put an isolation valve on the new tank....easier to test and change.
Do you have CI rads? The water content of the system determines the size of a new bladder tank.0 -
Yup, CI roads. 2.5in mains, 2-pipe direct return. Compression tank could even be from previous boiler, IDK.
Some idiot removed rad from kitchen and replaced with fin tube baseboard. Last connection off mains, kitchen always cold. Will be putting kitchen on it's own zone, adding kickspace heater if necessary.Mark
Indiana PA0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements