W.McLain Ultra 310 Series 2 control module conversion to series 4 U-Control
PlumbErwin
Member Posts: 1
So here it goes, first post.......
Working on a Ultra 310 Series 2 today. Found out control module failed. Got new control, opened box and "OH SNAP!!" No more Honeywell......
Spent the day installing the new control. Went to fire up and getting a error of "open limits". Figured out that the new module needs the Supply and Return Sensors (they didnt come with the new U-Control). Those are on the way, will install and hopefully the new control module will light up blue and stay blue. Boiler is just running hot with primary loop circulation.
Anyone have any helpful additional advice for me?
Working on a Ultra 310 Series 2 today. Found out control module failed. Got new control, opened box and "OH SNAP!!" No more Honeywell......
Spent the day installing the new control. Went to fire up and getting a error of "open limits". Figured out that the new module needs the Supply and Return Sensors (they didnt come with the new U-Control). Those are on the way, will install and hopefully the new control module will light up blue and stay blue. Boiler is just running hot with primary loop circulation.
Anyone have any helpful additional advice for me?
0
Comments
-
The Series 2 the limits are pretty brittle. Maybe order a full maintenance kit.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 915 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements