Wiring help

Options
jfpcan
jfpcan Member Posts: 1
edited June 2021 in THE MAIN WALL
Hello i have a taco zvc 404-4 zone controller my problem i have no zone valve motor just manual open close. Do i need to change my controller on can i somehow wire this one up to work without valve zones

Comments

  • Alan (California Radiant) Forbes
    Options
    So, you have one zone, one thermostat and one pump? No zone valves?

    How did you end up with a zone valve control and no zone valves to control?
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Dave H_2
    Dave H_2 Member Posts: 556
    Options
    If you have what Alan said, then you do have the wrong controller, a Switching Relay (SR) would have been correct to use.

    However, since you already have the ZVC controller, then yes, you can make it work.

    Thermostat wire to TT (pick one, TT 1-4)

    Circulator is going the pump relay on the lower right corner. Follow wiring diagram on the cover, the relay has no power there, you need to add 120v power there.

    Now following wherever you placed the thermostat (1-4), put a jumper wire across 3 and 4 on the zone valve side.

    The Zone Valve Controller with now act as a Single Zone Switching Relay!
    Dave H