Slant/Fin hot water shower issue
vish89
Member Posts: 5
I have a Slant/Fin sealed combustion boiler model no. LX-85A with a storage tank.
After about 8-9 minutes, the hot water basically turns cold/lukewarm. The domestic hot water supply setting is set at 160F.
What is my issue here?
thanks in advance.
thanks in advance.
0
Comments
-
This is the beginning of an algebra problem where you don't have all the variables We already know that 1 BTU will raise the temperature of 1 pound of water 1 degree farenheight. We also know that there is a maximum of 85,000 BTUs available in any given hour. We can assume the boiler will use those BTUs to transfer to the water at an efficiency rate of about 94%. We also know that water weighs about 8 pounds 6 ounces. With this information, we can calculate what amount of water will be heated from any given temperature to any other given temperature in any given time frame. Simply put you can make about 2.7 gallons of water change from 58°F to 118°F every minute.
The other variables are the amount of water stored in the tank, the lag time from the water tank temperature sensor indicating the need for the burner to operate, if the burner is operating at full capacity and if there is any off cycling during the need to make hot water.
If you are drawing more than 2.7 gallons per minute, and the burner is not activated on a timely basis and the burner does not operate at full output, then you will deplete the hot water in a short time frame.
Now that the math problem has started, let's fill in the blanks or variables.
1. What size pipe connects the boiler water to the indirect tank heat exchanger?
2. What is the boiler water temperature high limit set for?
3. What is the HOT water tank thermostat connected to?
a. Zone valve,
b. Zone Valve Control panel,
c. Circulator pump,
d. Circulator zone panel,
e. DHW terminals on the Slantfin Boiler Controller,
f. Other.
4. What size is the DWH tank? (or model number)
5. Finally, We like pictures. lots of pictures. From far enough away to see the pipes and how the boiler is connected to the water tank and the rest of the system. From several different angles.
If you can provide us with the info, and we can go further with the solution.
Yours Truly,
Mr.ED
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
0 -
Hi Mr. ED, for some reason it is not allowing me to post the pictures to this website. Do you have an email that I can you to the pictures too?0
-
0 -
0 -
The aquastat on the storage tank is set at 160F you say? If so, although the storage tank is on the small side (30 gallons?) it should have decent capacity for more than 9 minutes of consumption. A mixing valve added to the storage tank should be there, a 160F is very hot and the mixing valve will make the small tank perform like a much bigger one.1
-
Ctoilman said:The aquastat on the storage tank is set at 160F you say? If so, although the storage tank is on the small side (30 gallons?) it should have decent capacity for more than 9 minutes of consumption. A mixing valve added to the storage tank should be there, a 160F is very hot and the mixing valve will make the small tank perform like a much bigger one.And thanks for the response!0
-
-
Thank you for the input, I will look into it0
-
Is that a rebranded 20 gallon superstore? The transfer rate of the coil may also be a limiting factor.0
-
mattmia2 said:Is that a rebranded 20 gallon superstore? The transfer rate of the coil may also be a limiting factor.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements