LP gas fired steam boiler with induced draft
Schreyer
Schreyer Member Posts: 3
I've been looking for an LP gas fired steam boiler with induced draft. The chimney is in bad shape and needs to be removed. It would replace a Burnham oil fired steam boiler rated at 156 MBH with 488 sq ft steam.
    EBEBRATT-Ed Member Posts: 20,486
    Can you fix the chimney enough to put a liner in it? I don't believe anyone makes a steam boiler with induced draft.
    You could power vent a natural draft boiler through the side wall
  • Schreyer
    The chimney's problem is it's poor foundation. I have it strapped to the house just to keep it from falling over.
    The Burnham Independence PV is a gas boiler with induced draft but it only comes in natural gas and there is no conversion kit.
    I have heard that exterior power vents can be noisy and are susceptible to the weather.
    Thank you for your suggestions.
  • dopey27177
    dopey27177 Member Posts: 916
    Fix The chimney.
    Most economical way is to remove the masonry chimney and replace with a double lined stainless steel chimney.
    That chimney comes with kits to secure it to any building surface.
    A clean chimney will prevent any possibility of CO poisoning.
    Jake