Rating on fitzgibbons boiler
I am trying to find a rating on a fitzgibbons boiler RM-533f. have found the 530 and 550 but not the 533. was installed in 1960 according to church construction date. help would be most kind.
DCW
  • delta T
    delta T Posts: 884
    Check the burner orifices, see if there is a number on them (assuming this is NG or LP). If you can get that number and count the burners we can give you an input rating. Typically, for that vintage, 80% or input rating is output rating.
    Steamhead Posts: 18,942
    Is this a steam or hot-water system?
    Semi-retired
    EBEBRATT-Ed Posts: 21,091
    Fitzgibbons
    Has been long gone. Is there any rating on the name plate such as sq feet of heating surface? If you can post some pictures it will help.
    There are way to calculate the approximate capacity such as counting the fire tubes and there diameter to determine the sq feet of heating surface.
    In this age you will probably be better served by doing a heat loss of the building and starting from scratch as all old boiler were over sized.
    The other way that works is by looking at your fuel bills.
    And the gas or oil burner input would help.
    Is this hot water or steam??
  • DaleW
    DaleW Posts: 6
    water system, no other labels on boiler. has a powerflame gas burner in place of the old oil .
  • bburd
    bburd Posts: 1,326
    Clocking the gas meter would at least tell you the firing rate of the burner.
    Bburd
  • retiredguy
    retiredguy Posts: 1,105
    edited March 2021
    If you have any service records from companies that serviced that unit, they may be able to give you an idea of the size of the boiler. Also, if you can find out the company that installed the burner, they may be able to help since they would have had to know the boiler's approximate size. The rating plate on that Power flame Burner will give you it's approximate firing rate and the size of the burner. Last, mention just where you are and someone on this site may be able to give you names of a company in your area that can help.
